    batmon18's Avatar
    batmon18 Guest
    Calculating Tonnage of refrigeration machine
    Hello all, i'm an engineering intern trying to calculate the tonnage of an electric brine refrigeration machine. I read the info on the motor and it's a: 223 amp motor, 2300 volts, 900 HP. Anyone know how to calculate tonnage?
    Aug 2005
    5,327
    Re: Calculating Tonnage of refrigeration machine
    That will not work. You need to find the operating conditions of the refrigeration system and a copy f the compressor manufacturers performance data.
    Anything else is just a wild guess.
    batmon18's Avatar
    batmon18 Guest
    I have a list of real-time operating conditions:
    Comp TEJ Bearing Temp Comp SEJ Bearing Temp Comp Thrust Bearing Temp Comp Oil Reservoir Press Comp Oil Temp Comp BRG Oil Supply Comp Back of Seal Oil Press Comp Oil Diff. Press Comp Discharge Gas Temp Comp Bearing Oil Supply Temp Gear/Motor Oil Supply Temp Motor Amps Cond. Enter Water Temp Cond. Exit Water Temp Cond Refrigerant Temp Cond Refrig. Press Evap Refrig. Press Brine Entering Temp Brine Leaving Temp Main Brine Loop Temp Evap Refrig. Temp Economizer Refrig. Temp Control Air Press Local Temp Set Pt. PID Out
    I'm wondering if I can use the motor amps and voltage to get HP and use that to calculate tonnage..
    batmon18's Avatar
    batmon18 Guest
    Sorry, here it is in list form:
    Comp Oil Reservoir Pressure
    Comp Oil Temp
    Comp BRG Oil Supply
    Motor Amps
    Cond Refrig. Press
    Evap Refrig. Press
    Brine Entering Temp
    Brine Leaving Temp
    Evap Refrig. Temp
    Control Air Press
    Local Temp Set Pt.
    PID Out
    Aug 2005
    5,327
    all you need are these:
    Cond Refrig. Press
    Evap Refrig. Press
    Convert the pressures to the saturation temperatures for the specific refrigerant used in the compressor. Now look these temperatures up on the compressor manufacturers performance charts. They list the compressor performance based on saturated inlet (suction) and condensing temperatures.
    batmon18's Avatar
    batmon18 Guest
    Thumbs up Re: Calculating Tonnage of refrigeration machine
    Cond Refrig. Press
    Evap Refrig. Press
    Great! Thanks so much for the help
    Jun 2009
    Here is what I do. First you need to have the manufactures performance data at 25 different Suction and discharge temperatures. These are laid out in a matrix. 5 suction by 5 discharge. These will be shown as Tons of refrigeration and Brake Horse Power. By running these numbers through a nasty equation you can come out with that compressors performance at any given suction and discharge temperature. If the compressor has a VFD just use the speed as a direct multiplier. If the compressor is a screw and is running at a part load it is not a linear conversion. You would need to find out how the slide valve affects capacity at different positions. So 90% slide valve does not mean 90% capacity. There is a nasty equation for that too. Recips are linear.
  1. advanced refrigeration technology
    Last Post: 16-02-2011, 05:22 PM
  2. Replies: 8
    Last Post: 23-04-2008, 06:48 PM
  3. Calculating Refrigeration load for Cold room
    By Sridhar1312 in forum CO2
    Last Post: 16-01-2008, 12:06 AM
Tags for this Thread