Thread: burn outs
    Jan 2007
    59
    145
    burn outs
    I have a small Liebert mini mate. We had a leak in it we put dye in to find leak. System had burned out after dye was put in. There was a coating on every piece of the high side components. Compressor, piping, txv and plate condenser had to be changed. my question is did the dye cause the burnout? (create an acid enviroment) I have seen burn outs, but not to this extent. The refrigerant is 407C,poe oil. The smell was horrific.
    Oct 2008
    mallorca, spain,
    75
    768
    Re: burn outs
    we have been worned about adding stuff like this , in reality why add something when there are better ways of finding a leak without the risk of this problem you have experienced
    all the best=
    Sep 2003
    ISRAEL
    72
    4,248
    Re: burn outs
    Was it written on the dye can what kind of refrigeration oil it is good for?
    Oct 2001
    Nottingham UK
    5,667
    Re: burn outs
    Quote Originally Posted by joe magee View Post
    Was the oil a black colour?
    Jan 2007
    59
    145
    Re: burn outs
    The oil was green. The dye was the yellow jacket brand. You use the uv light. The coating looked like green scale. Like what you would see on the outside of a leaking water pipe. It is acceptable for use with poe oil. The lieberts units use a three minute time delay on the low side. If the unit is low on charge it will run in a vacuum before it times out allowing non condensilbles to enter the system. My guess is this is what happened. An enviroment for an acid condition was created. The addition of the dye(which I did not add) might have caused a bad condition to get worse. I have used the dye in the past with mixed results.
    Oct 2001
    Nottingham UK
    5,667
    Re: burn outs
    We've encountered system failures on R407C where the windings have burnt out.
    When you open the system, the smell in horrendous and the oil is a thick black sludge. From our experience this is due to poor installation practices and moisture in the system.
  1. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Last Post: 07-05-2010, 09:24 AM
  2. Frequent compressor burn outs
    By askannan in forum Trouble Shooting
    Last Post: 17-04-2008, 08:05 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Motor burn outs
    By bernard in forum Industrial Compressors
    Last Post: 25-06-2005, 11:00 PM
  5. Burn out procedures
    By reggie in forum Fundamentals
    Last Post: 22-01-2003, 06:06 PM