air conditioning a kitchen
We got a call to to look at a temporary kitchen which is in a marquee.
The size is about 12 x 15m square and 6m at the centre.
As it's a full working kitchen for approx 100 workers it has 2 coldrooms and one freezer room plus all the usual ovens hobs grills etc etc.
So where on earth would we start to size the gaff? Obviously we aren't looking to make it 20 deg's but on friday it was 37 in places and they were worried on H&S grounds.
-
30-05-2009, 03:38 PM #2
Re: air conditioning a kitchen
Hi. You have not mentioned what for exhaust ventilation they have.
-
30-05-2009, 03:44 PM #3
Re: air conditioning a kitchen
Aproxim 100 souls in such a space is a bit too much too.
-
30-05-2009, 06:38 PM #4
Re: air conditioning a kitchen
As it's temporary, and contains a lot of radiant heat devices, (cookers, hobs, grilles etc.) the only thing in my opinion would be a full fresh air system. Let the cooking extract determine the amount of air volume you require and work from there.
If you keep the input air just short of the extract volume, say 10% you will prevent cooking smells spilling out.
I would aim for a supply air temperature of between 15 - 18C, using staging for capacity control.
-
30-05-2009, 06:48 PM #5
Re: air conditioning a kitchen
Only air ducts, fans, their grilles have been very possibly neglected and now are fairly covered with grease.
-
31-05-2009, 10:20 AM #6
-
31-05-2009, 10:29 AM #7
Re: air conditioning a kitchen
We were thinking of one or those marquee coolers you see at various outdoor events. I doubt we will maintain a temperature but hope to take the top off the temps. The fridges and freezers are struggling and chef is worried about food poisoning.
We guessed 100kw but will suggest 40kw
-
31-05-2009, 04:18 PM #8
Re: air conditioning a kitchen
big evaporative cooler, go all outside air , purge the heat out of it
Take the V out of HVAC and you are left with a HAC job
-
31-05-2009, 04:22 PM #9
Re: air conditioning a kitchen
this is a tent?
Take the V out of HVAC and you are left with a HAC job
-
31-05-2009, 05:18 PM #10
Re: air conditioning a kitchen
Evaporative cooler is no good in kitchens, its humid enough as it is .
A 100% fresh air AC unit will do the job better and a few extract air fans on the other side.
Ducts tend to get covered with oil and kitchen dirt.
-
31-05-2009, 11:06 PM #11
Re: air conditioning a kitchen
This sounds like a tent, and it traps the heat, so too bad they do not have roof vents in a tent. If they do have hoods for the cooklines then the hoods are pulling the humidty generated by cooking out of the space, but there is still radiant heat from the cookline and items like refrigerators etc give off heat as well.
Evaporative cooling is ideally a 100% outside air system. It has nothing to do with the humidity generated inside of a kitchen as it is a displacement effect.
Evaporative cooling applied to recirculated indoor air is a humidifier, you want to humidity the outside air to cool it off, blow it into a hot space, cools the space and then displaces humid air out of the space.
A rainy climate like the UK gets perceived as humid but when you look at dewpoints you get in the outdoor air, it is not a humidity challenge at all.
You can get huge tents to double as mess halls, ballrooms etc, seen people use duct sox and a couple big package units for this type of applicationLast edited by Abby Normal; 31-05-2009 at 11:12 PM.
Take the V out of HVAC and you are left with a HAC job
-
01-06-2009, 08:46 AM #12
Re: air conditioning a kitchen
Here is a pic of the tent.
-
01-06-2009, 01:23 PM #13
Re: air conditioning a kitchen
It traps the heat
Gable vents on each end would make a huge difference, even if one end was a just a prop fan exhaust and the other end was a filtered intake.
You may want to try a series of spot coolers as well, something that gets air directed to where the people are working
Get the duct sox with the nozzles, have the nozzles aimed at the floor of the aisles seems like there are two aisles going down the length, you need to do some grade school geometry here. Blow evaporatlvely cooled outsde air into the duct sox. It is going to spot cool the people in the aisles. Have relief vents on the two gabled walls up high. You will be spot cooling the people and purging out the heat at the same time.
Trying to put something inside that recirculates air is going to need twice the capacity as something that purges.
Best attempt for recirculating air is spot coolers, just you direct them to where the people are working.Last edited by Abby Normal; 01-06-2009 at 01:33 PM.
Take the V out of HVAC and you are left with a HAC job
-
01-06-2009, 01:52 PM #14
Re: air conditioning a kitchen
I think with the UK climate, even filtered outside air ( instead of cooled air) getting blown down at those aisles will be infinitely better than what it is like in there now, the convection is going to cool the people working and you are still pruging the heat out of the tent.
Right now it has to be getting a lot hotter inside than it is outside.
It would be like the difference between a sweltering day in still air vs what is perceived as a cool breeze. If you ever visited anywhere hot and humid, this would be hitting homeTake the V out of HVAC and you are left with a HAC job
-
01-06-2009, 05:47 PM #15
Re: air conditioning a kitchen
To add a trifle to the so exhaustive comments - maybe also it is worth cover the (at least the southern part of the) construction, which seems to be half-transparent, with sun light reflective foily cover (like they put on window glasses)?
-
01-06-2009, 08:53 PM #16
Re: air conditioning a kitchen
As solar rays may also drive up heat inside - at sunny days (greenhouse). I dont know however nothing about the material these tents are made of - it may already be, "ray repelling."
-
01-06-2009, 09:07 PM #17
Re: air conditioning a kitchen
could this type of fabric ducting help you out? attached to some large split ducted units utilising fresh air?
http://www.refrigeration-engineer.co...&pictureid=706
al
-
01-06-2009, 10:03 PM #18
Re: air conditioning a kitchen
Maybe, also, provide separate extraction line(s) for the off air of the condensers - both of the cold rooms and the freezer?
-
01-06-2009, 10:28 PM #19
Re: air conditioning a kitchen
I agree with the above comments, lots of fresh air and if possible some extract fans. You need to pull that heat out and introduce fresh outside air that is always going to be cooler than the 37C you mentioned in places.
The fabric ducting sounds good as well and will be filtered quite well too.
-
02-06-2009, 12:16 AM #20
Re: air conditioning a kitchen
Take the V out of HVAC and you are left with a HAC job
-
02-06-2009, 02:47 AM #21
Re: air conditioning a kitchen
im with abby,big swampy with lots of air and general relief,hood design affects the effect also.cant say ive seen refrigerated used in a commercial situation
mmm to beer or not to beer...........lets drink breakfast
-
03-06-2009, 01:13 AM #22
Re: air conditioning a kitchen
Phew, a tricky one. Being temporary, no one will want to pay big time for a proper hood solution and aircon supply. Big money.
Practically, you should look at extracting from high level. Get a long duct through the tent, under the apex, and a big fan on the outside. (possibly a bifurcated fan, with all that greasy air.)
You could put a couple of those big 15kW portable aircon units (telephone box with hoses out the top/front) in there to help with the general air temperature. More expensively, you could hire a chiller and AHU to push cool air into the tent. (Andrews Hire?)
You could also put a few desktop fans around the place (but secure so they don't fall into the chip-friar) to deal with that radiant heat from the kitchen equipment. But, the cooks are used to this kind of thing.Last edited by Makeit go Right; 03-06-2009 at 10:23 PM. Reason: Frank
-
03-06-2009, 02:15 AM #23
Re: air conditioning a kitchen
Lots of fresh air, minimal pressurization,natural exhaust through openings.
magoo
-
03-06-2009, 04:42 AM #24
Re: air conditioning a kitchen
come to think of it,if this was aust it probably wouldnt be there.me thinks the powers that be would shut it down.pics of wash,cooking areas would be interesting to see
mmm to beer or not to beer...........lets drink breakfast
-
03-06-2009, 10:05 AM #25
-
03-06-2009, 08:37 PM #26
Re: air conditioning a kitchen
-
03-06-2009, 08:46 PM #27
Re: air conditioning a kitchen
by the looks of the situation due to the temperature at which the col rooms are it seems they are under more load than they should be.
you would be looking at at least 50kw which works out at 250 watts persquare meter, with no insulation on the tent.
Air changes at the top of the tent and cooling from low level shoul do the trick, i can't see it being cheap though.
-
04-06-2009, 03:02 AM #28
Re: air conditioning a kitchen
first time ive used a quote will see what happens. building codes & as you mentioned health,all temporary tents i have seen are scout camps,sausage sizzles and small events(one could say the clipsal 500 is small event as is only a few days).but apart from getting away from the point i rest with whats said about evaporative a/c.i imagine your ground water temperature would be fairly cool also.bon appetite
mmm to beer or not to beer...........lets drink breakfast
Similar Threads
-
Business opportunity developing a wood fueled air conditioning system
By Woodman in forum CommercialReplies: 11Last Post: 13-08-2008, 01:22 PM -
Unique cooling system Port-A-Cool replaces air conditioning
By LC-Europe in forum New TechnologiesReplies: 20Last Post: 30-01-2008, 08:29 AM -
Certificate in Mobile Air Conditioning Systems
By Tony in forum TrainingReplies: 2Last Post: 01-07-2007, 04:30 PM -
How do you manage to "cool" a kitchen?
By Abe in forum Technical DiscussionsReplies: 11Last Post: 19-08-2002, 06:08 PM