    We got a call to to look at a temporary kitchen which is in a marquee.

    The size is about 12 x 15m square and 6m at the centre.

    As it's a full working kitchen for approx 100 workers it has 2 coldrooms and one freezer room plus all the usual ovens hobs grills etc etc.

    So where on earth would we start to size the gaff? Obviously we aren't looking to make it 20 deg's but on friday it was 37 in places and they were worried on H&S grounds.



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: air conditioning a kitchen

    Hi. You have not mentioned what for exhaust ventilation they have.

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: air conditioning a kitchen

    Aproxim 100 souls in such a space is a bit too much too.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: air conditioning a kitchen

    As it's temporary, and contains a lot of radiant heat devices, (cookers, hobs, grilles etc.) the only thing in my opinion would be a full fresh air system. Let the cooking extract determine the amount of air volume you require and work from there.

    If you keep the input air just short of the extract volume, say 10% you will prevent cooking smells spilling out.

    I would aim for a supply air temperature of between 15 - 18C, using staging for capacity control.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: air conditioning a kitchen

    Only air ducts, fans, their grilles have been very possibly neglected and now are fairly covered with grease.

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: air conditioning a kitchen

    Quote Originally Posted by Yuri B. View Post
    Aproxim 100 souls in such a space is a bit too much too.
    It's a kitch to provide food for 100 workers. It is not a restaurant space.

  7. #7
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: air conditioning a kitchen

    Quote Originally Posted by frank View Post
    As it's temporary, and contains a lot of radiant heat devices, (cookers, hobs, grilles etc.) the only thing in my opinion would be a full fresh air system. Let the cooking extract determine the amount of air volume you require and work from there.

    If you keep the input air just short of the extract volume, say 10% you will prevent cooking smells spilling out.

    I would aim for a supply air temperature of between 15 - 18C, using staging for capacity control.
    We were thinking of one or those marquee coolers you see at various outdoor events. I doubt we will maintain a temperature but hope to take the top off the temps. The fridges and freezers are struggling and chef is worried about food poisoning.

    We guessed 100kw but will suggest 40kw

  8. #8
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: air conditioning a kitchen

    big evaporative cooler, go all outside air , purge the heat out of it
    Take the V out of HVAC and you are left with a HAC job

  9. #9
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: air conditioning a kitchen

    this is a tent?
    Take the V out of HVAC and you are left with a HAC job

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: air conditioning a kitchen

    Evaporative cooler is no good in kitchens, its humid enough as it is .

    A 100% fresh air AC unit will do the job better and a few extract air fans on the other side.

    Ducts tend to get covered with oil and kitchen dirt.

  11. #11
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: air conditioning a kitchen

    Quote Originally Posted by chemi-cool View Post
    Evaporative cooler is no good in kitchens, its humid enough as it is .

    A 100% fresh air AC unit will do the job better and a few extract air fans on the other side.

    Ducts tend to get covered with oil and kitchen dirt.
    This sounds like a tent, and it traps the heat, so too bad they do not have roof vents in a tent. If they do have hoods for the cooklines then the hoods are pulling the humidty generated by cooking out of the space, but there is still radiant heat from the cookline and items like refrigerators etc give off heat as well.

    Evaporative cooling is ideally a 100% outside air system. It has nothing to do with the humidity generated inside of a kitchen as it is a displacement effect.

    Evaporative cooling applied to recirculated indoor air is a humidifier, you want to humidity the outside air to cool it off, blow it into a hot space, cools the space and then displaces humid air out of the space.

    A rainy climate like the UK gets perceived as humid but when you look at dewpoints you get in the outdoor air, it is not a humidity challenge at all.

    You can get huge tents to double as mess halls, ballrooms etc, seen people use duct sox and a couple big package units for this type of application
    Last edited by Abby Normal; 31-05-2009 at 11:12 PM.
    Take the V out of HVAC and you are left with a HAC job

  12. #12
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: air conditioning a kitchen

    Here is a pic of the tent.
    Attached Images Attached Images

  13. #13
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: air conditioning a kitchen

    It traps the heat

    Gable vents on each end would make a huge difference, even if one end was a just a prop fan exhaust and the other end was a filtered intake.

    You may want to try a series of spot coolers as well, something that gets air directed to where the people are working

    Get the duct sox with the nozzles, have the nozzles aimed at the floor of the aisles seems like there are two aisles going down the length, you need to do some grade school geometry here. Blow evaporatlvely cooled outsde air into the duct sox. It is going to spot cool the people in the aisles. Have relief vents on the two gabled walls up high. You will be spot cooling the people and purging out the heat at the same time.

    Trying to put something inside that recirculates air is going to need twice the capacity as something that purges.

    Best attempt for recirculating air is spot coolers, just you direct them to where the people are working.
    Last edited by Abby Normal; 01-06-2009 at 01:33 PM.
    Take the V out of HVAC and you are left with a HAC job

  14. #14
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: air conditioning a kitchen

    I think with the UK climate, even filtered outside air ( instead of cooled air) getting blown down at those aisles will be infinitely better than what it is like in there now, the convection is going to cool the people working and you are still pruging the heat out of the tent.

    Right now it has to be getting a lot hotter inside than it is outside.

    It would be like the difference between a sweltering day in still air vs what is perceived as a cool breeze. If you ever visited anywhere hot and humid, this would be hitting home
    Take the V out of HVAC and you are left with a HAC job

  15. #15
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: air conditioning a kitchen

    To add a trifle to the so exhaustive comments - maybe also it is worth cover the (at least the southern part of the) construction, which seems to be half-transparent, with sun light reflective foily cover (like they put on window glasses)?

  16. #16
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: air conditioning a kitchen

    As solar rays may also drive up heat inside - at sunny days (greenhouse). I dont know however nothing about the material these tents are made of - it may already be, "ray repelling."

  17. #17
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: air conditioning a kitchen

    could this type of fabric ducting help you out? attached to some large split ducted units utilising fresh air?

    http://www.refrigeration-engineer.co...&pictureid=706




    al

  18. #18
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: air conditioning a kitchen

    Maybe, also, provide separate extraction line(s) for the off air of the condensers - both of the cold rooms and the freezer?

  19. #19
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: air conditioning a kitchen

    I agree with the above comments, lots of fresh air and if possible some extract fans. You need to pull that heat out and introduce fresh outside air that is always going to be cooler than the 37C you mentioned in places.

    The fabric ducting sounds good as well and will be filtered quite well too.

  20. #20
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: air conditioning a kitchen

    Quote Originally Posted by al View Post
    could this type of fabric ducting help you out? attached to some large split ducted units utilising fresh air?

    http://www.refrigeration-engineer.co...&pictureid=706




    al
    get them with nozzles, to blast the air down and spot cool the occupants, you would not want the diffuse air leaking out all over the place.

    You push air down it will force air up and if you have high vents, you get high level air moving out
    Take the V out of HVAC and you are left with a HAC job

  21. #21
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: air conditioning a kitchen

    im with abby,big swampy with lots of air and general relief,hood design affects the effect also.cant say ive seen refrigerated used in a commercial situation
    mmm to beer or not to beer...........lets drink breakfast

  22. #22
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: air conditioning a kitchen

    Phew, a tricky one. Being temporary, no one will want to pay big time for a proper hood solution and aircon supply. Big money.

    Practically, you should look at extracting from high level. Get a long duct through the tent, under the apex, and a big fan on the outside. (possibly a bifurcated fan, with all that greasy air.)

    You could put a couple of those big 15kW portable aircon units (telephone box with hoses out the top/front) in there to help with the general air temperature. More expensively, you could hire a chiller and AHU to push cool air into the tent. (Andrews Hire?)

    You could also put a few desktop fans around the place (but secure so they don't fall into the chip-friar) to deal with that radiant heat from the kitchen equipment. But, the cooks are used to this kind of thing.
    Last edited by Makeit go Right; 03-06-2009 at 10:23 PM. Reason: Frank

  23. #23
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: air conditioning a kitchen

    Lots of fresh air, minimal pressurization,natural exhaust through openings.
    magoo

  24. #24
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: air conditioning a kitchen

    come to think of it,if this was aust it probably wouldnt be there.me thinks the powers that be would shut it down.pics of wash,cooking areas would be interesting to see
    mmm to beer or not to beer...........lets drink breakfast

  25. #25
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: air conditioning a kitchen

    Quote Originally Posted by lowcool View Post
    come to think of it,if this was aust it probably wouldnt be there.me thinks the powers that be would shut it down.pics of wash,cooking areas would be interesting to see

    Why would they shut down a kitchen?

  26. #26
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: air conditioning a kitchen

    Quote Originally Posted by Makeit go Right View Post
    . (Should be bifurcated, really.)
    Any idea why?
    Quote Originally Posted by Makeit go Right View Post
    You could put a couple of those big 15kW portable aircon units (telephone box with hoses out the top/front) in there for anyone sitting down (guess they sit off to the right hand side, yes?)
    I thought we were talking about a kitchen???

    Quote Originally Posted by Makeit go Right View Post
    But it would be better to get some more tables and chairs so the diners can eat outside, once they collect their plateful from the cooks.
    Have we lost the plot a little?
    Quote Originally Posted by Makeit go Right View Post
    For the cooks -- poor souls -- they need lots of desktop fans that are not falling into the chip-friar. But, they are used to this kind of thing.
    Desktop fans in the kitchen....

  27. #27
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: air conditioning a kitchen

    by the looks of the situation due to the temperature at which the col rooms are it seems they are under more load than they should be.

    you would be looking at at least 50kw which works out at 250 watts persquare meter, with no insulation on the tent.
    Air changes at the top of the tent and cooling from low level shoul do the trick, i can't see it being cheap though.

  28. #28
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: air conditioning a kitchen

    Quote Originally Posted by multisync View Post
    Why would they shut down a kitchen?
    first time ive used a quote will see what happens. building codes & as you mentioned health,all temporary tents i have seen are scout camps,sausage sizzles and small events(one could say the clipsal 500 is small event as is only a few days).but apart from getting away from the point i rest with whats said about evaporative a/c.i imagine your ground water temperature would be fairly cool also.bon appetite
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. Replies: 11
    Last Post: 13-08-2008, 01:22 PM
  2. Unique cooling system Port-A-Cool replaces air conditioning
    By LC-Europe in forum New Technologies
    Replies: 20
    Last Post: 30-01-2008, 08:29 AM
  3. Replies: 2
    Last Post: 01-07-2007, 04:30 PM
  4. How do you manage to "cool" a kitchen?
    By Abe in forum Technical Discussions
    Replies: 11
    Last Post: 19-08-2002, 06:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •