Re: 4-stage cascade
It makes sense. Interestingly, playing with the bulb pressure allows to play with refrigerant charge of the system. For example, it is possible to achieve the same evap temperature with a moderate refrigerant charge but with a high bulb pressure than with more refrigerant in the circuit but with less pressure in the bulb. I've tested this yesterday and I have been able to run a system with less static pressure.
-
15-05-2011, 09:53 AM #53
Re: 4-stage cascade
I've removed the 3rd stage CPU evaporator CPEV because it was leaking by the screw, and replaced it by 1.75m of .8mm captube.
Evap out = -129.3C; it looks fairly accurate.
HSP: 1st stage at 10.5 bars, 2nd stage at 5 bars and 3rd stage at 13
Probes gave -50C for the 1st stage TXV and -85C for the 2nd stage TXV.
I didn't know why, but 3rd stage evaporator took a very long time to go down to about -117C and then lost nearly 20C within few seconds.... I was a bit puzzled. So I've tried different captube lengths to finally switch back to a CPEV.
Unfortunately, this new CPEV puts more load on the higher stages. 2nd stage R23 is not enough now. I'm considering doing the following:
- Replacing 1st stage R507 by R410 which would be better to condensate 2nd stage R1150
- Replacing 2nd stage R23 by R1150 which is needed in order to condensate 3rd stage R14
Similar Threads
-
r-23 low stage, cascade system
By johnny1 in forum RefrigerantsReplies: 8Last Post: 21-11-2009, 09:01 PM -
Building a 3 stage cascade
By NoL in forum CPU OverclockersReplies: 9Last Post: 27-03-2009, 08:42 PM -
3-stage cascade
By before in forum CPU OverclockersReplies: 47Last Post: 22-02-2009, 11:18 AM -
Single stage Vs 2 stage comp rack
By Kevin Yeo in forum Supermarket RefrigerationReplies: 0Last Post: 01-02-2007, 03:05 PM -
Regulation regarding hydrocarbons in an cascade
By DaBit in forum FundamentalsReplies: 4Last Post: 19-01-2004, 12:42 PM