    problem with volume on frick screw compressor



    Having trouble with Frick screw mod# RWF 11 222 E. At 0 percent load i have a volume of 5 but when the screw starts to load up my volume starts to drop to min. Vi of 2.2.When the compressor reaches 100 percent i get a message saying unload, increase volume on the micro it is showing that it is giving signal to increase but the Vi will only go to 2.88 Vi.Checked the wiring checked the solenoid every thing in normal but Vi will not increase. When the compressor is unloading my Vi will increase as my capacity decreases.Called Frick to ask them there input into the situation he asked me to give him the voltage readings for the slide vavle and slide stop valve. My voltages for capacity fully unloaded min. position i have voltage fo 3.8 v on the loaded max position voltage is 4.65, for the slide stop voltage at min. is 3.26 and at max is 4.53. Frick told me the voltage read by slide stop seems to be fine but capacity voltage seems out of whack. Told me the slide valve sensor probably faulty and causing me to have trouble with volume. I don't see how the capacity sensor or slide valve position can affect my volume was wondering if anybody has come across this problem.Sorry seems i posted this question in two places one in industrial and one in industrial compressors.
    Last edited by samlee12; 30-05-2009 at 11:40 AM.



  2. #2
    Join Date
    Aug 2009
    Location
    Australia
    Age
    47
    Posts
    10
    Rep Power
    0

    Re: problem with volume on frick screw compressor

    I have sim. Problem with frick 193l srew and the servo potentiometer should read 1k ohms at 0 % (red to white wire?) i reclaimed gas into the unload chamber and relieved out of the load chamber to get a ref.point

  3. #3
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: problem with volume on frick screw compressor

    What are the pressures you are working with? Have you tried calibrating the slide valve and slide stop? What type panel is it using Quantum or Plus panel? I would try calibrating them both and then see what happens. The slide valve has a lot to do with volume.
    Last edited by nh3wizard; 07-08-2009 at 04:15 PM. Reason: More info

  4. #4
    Join Date
    Dec 2008
    Location
    Moncton,N.B. Canada
    Age
    48
    Posts
    44
    Rep Power
    0

    Re: problem with volume on frick screw compressor

    not sure why this question was posted again. This question was posted quite awhile ago and had been answered by multiple people.All the other posts have seem to disappear, weird. anyway the problem turned out to be that i was trying to calibrate under high load and prevented machine from calibrating properly, coworker had figured this out and recalibrated under low load conditions and compressor is working fine.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: problem with volume on frick screw compressor

    Quote Originally Posted by samlee12 View Post
    not sure why this question was posted again. This question was posted quite awhile ago and had been answered by multiple people.All the other posts have seem to disappear, weird. anyway the problem turned out to be that i was trying to calibrate under high load and prevented machine from calibrating properly, coworker had figured this out and recalibrated under low load conditions and compressor is working fine.
    Thanks for the update- appreciated.
    Grizzly

Similar Threads

  1. screw verses reciprocating compressor
    By ukram in forum Industrial Compressors
    Replies: 14
    Last Post: 18-05-2009, 01:06 AM
  2. Compressor Knock problem
    By AC90 in forum New to RE
    Replies: 10
    Last Post: 11-05-2008, 04:26 PM
  3. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM
  4. Screw compressor (ATLAS GA510)
    By AndEdtec in forum Trouble Shooting
    Replies: 7
    Last Post: 21-07-2006, 08:34 PM
  5. One Half of a Part Wound Compressor Motor is Burnt
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 25-08-2003, 11:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •