    evap icing up



    Hi guys

    was at a job today where a third of the evaporater coil was iced up. it was a crafft package ac unit (window rattler)
    there was too much heat in the room and this unit is struggling and is undersized.

    My question is can some explain why the top of the evap iced up and what caused this.

    i understand that the compressor will be permantly on as temp in the room will never be maintained but would like to know why it ices up as it did or why it ices up!

    thanks in advance
    moondawn



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: evap icing up

    Most probably, it has overworked, overheated, and now just beginning to lose its refrigerant charge. Soon it will be dead if competent urgent measures are not undertaken. Now it is necessary to switch it off.

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: evap icing up

    Filters, airflow and gas charge. Check all them and determine the problem. Also air flow on and off values.

  4. #4
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    58
    Posts
    723
    Rep Power
    22

    Re: evap icing up

    Add to that the high humidity of the UK for the realatively low temperature.... Had an LG that used to do that but it was easily fixed with a sledge hammer

    No, Really... When I replaced it FOC (My fault for selecting the wrong unit) and replaced it with a Sanyo (I only ever visit that unit for regular servicing) I placed the LG on my drive and beat the daylights out of it Saying " You wont be doing that to me again" in a very Basil Fawlty way.... My neghbours are used to my little ways now
    Karl

  5. #5
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: evap icing up

    hi all

    thanks for the replies

    the unit once defrosted, checked the system and it seemed to work well just could not cope with the demand. i just wondered why the icing would start cos its undersized. a walkthrough of how that process happens with a unit over working?


    cheers
    moondawn

  6. #6
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: evap icing up

    Were filters clogged or clean when you found the ice ?

  7. #7
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: evap icing up

    Your heavy struggling unit works with very large supeheat, compressor not cooled, heat gathers, head temp rise and rise.
    HFC's molecules which are much less than earlier refrigerants's are bit by bit leaving the overheated system through the pores in copper pipes and loaded connections (even not speaking about the flair connections).
    Evap icing up happens most offen at morning hours (if unit was left working). Outside air temp drops, pressures drop, at some moment evap pressure reaches such a low level (due to the lack of *****), that not only evap's coil - the return pipe may cover in ice. The process is aggreviated if, by that, the filter has been neglected.
    If you do not measure suction pressure and superheat now soon you will lose your rattler.

  8. #8
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: evap icing up

    Due not to the lack but shortage of *****, of course.

  9. #9
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: evap icing up

    Quote Originally Posted by Yuri B. View Post
    Were filters clogged or clean when you found the ice ?
    Filters were spotless mate.
    the unit had been serviced recently and the engineer who serviced it noticed they had added more equipment into the COMMS ROOM.

    Because of this the window rattler is overworking.

    i aint sure that the unit is leaking refigerant more that it is undersized and therefor working every day every second of the day which odviously is not good.

    cheers
    moondawn

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: evap icing up

    Excessive load would tend to prevent the coil from frosting, not cause it to frost.

    Insufficient airflow would tend to frost the coil evenly.

    Insufficient charge would tend to frost the coil from the top down.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: evap icing up

    Quote Originally Posted by moondawn View Post
    i aint sure that the unit is leaking refigerant more that it is undersized and therefor working every day every second of the day which odviously is not good.
    Actually, stopping and starting is harder on a system than running continuously.

  12. #12
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: evap icing up

    Quote Originally Posted by Gary View Post
    Excessive load would tend to prevent the coil from frosting, not cause it to frost.

    Insufficient airflow would tend to frost the coil evenly.

    Insufficient charge would tend to frost the coil from the top down.
    hi gary thanks for your input

    ok so its sounding as if this unit does not have enough refrigerant.

    the top third of the coil was iced solid.

    i could not understand why the unit iced up so glad i asked the question thanks guys

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: evap icing up

    Quote Originally Posted by moondawn View Post
    ok so its sounding as if this unit does not have enough refrigerant.
    It would be more accurate to say that it doesn't have enough refrigerant in the low side of the system.

    This could mean that the unit is undercharged... but it could also mean that the unit has a partial restriction, not allowing sufficient liquid to flow from the high side to the low side.

  14. #14
    Join Date
    Mar 2008
    Location
    Romania
    Age
    43
    Posts
    44
    Rep Power
    0

    Re: evap icing up

    Check the filter drier in the liquid line if it has one.

  15. #15
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: evap icing up

    Quote Originally Posted by Gary View Post
    It would be more accurate to say that it doesn't have enough refrigerant in the low side of the system.

    This could mean that the unit is undercharged... but it could also mean that the unit has a partial restriction, not allowing sufficient liquid to flow from the high side to the low side.
    yes very true gary as the icing is appaearing in the low side so after the expansion device it could have a problem.

    thanks for all your help and the others too.

    moondawn

  16. #16
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: evap icing up

    is it 134a refrigerant per chance
    mmm to beer or not to beer...........lets drink breakfast

  17. #17
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: evap icing up

    Short of gas
    Last edited by Magoo; 02-06-2009 at 03:10 AM.

  18. #18
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: evap icing up

    Quote Originally Posted by lowcool View Post
    is it 134a refrigerant per chance
    hi there the gas is r407c

  19. #19
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: evap icing up

    Quote Originally Posted by moondawn View Post
    hi there the gas is r407c
    probably rules out capillary restriction,your left with gas shortage,system restriction or slight compressor inefficiency,time to fit the gauges and do your job.
    mmm to beer or not to beer...........lets drink breakfast

  20. #20
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: evap icing up

    not been back to site since.

    will update if i go back

    thanks all

  21. #21
    Victor537Boston's Avatar
    Victor537Boston Guest

    Re: evap icing up

    Quote Originally Posted by rude View Post
    Filters, airflow and gas charge. Check all them and determine the problem. Also air flow on and off values.
    I agree you need to know what the pressures are most importantly as well as superheat and subcooling. Sounds to me low on gas, or the valves on the compressor are on the way so the compression ratio is not at its prime anymore.

Similar Threads

  1. Outdoor coil icing up...
    By airflo in forum Heat Pumps
    Replies: 18
    Last Post: 28-10-2008, 07:12 PM
  2. iced up evap coil
    By wilks in forum Fundamentals
    Replies: 6
    Last Post: 31-08-2007, 09:15 PM
  3. Compressor suction icing up on cold room set up
    By Leviathan in forum Trouble Shooting
    Replies: 9
    Last Post: 02-06-2007, 05:08 AM
  4. Krack Evaporator Icing
    By Rob@goldcoast in forum Technical Discussions
    Replies: 11
    Last Post: 15-08-2006, 02:53 AM
  5. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 04:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •