    Moving a cold room



    I am moving a coldroom from one premises to another. I pumped the unit down closed in the suction, cut the pipes. Took down cooler etc....
    Question when I put it all back together again do I have to use a reclaim plant to remove the refrigerant from the condensing unit so I can pressure test the system. I obviously dont want to get nitrogen mixing with the refrigerant.



  2. #2
    Join Date
    Jan 2009
    Location
    sunny norfolk
    Posts
    81
    Rep Power
    16

    Re: Moving a cold room

    just out of intrest, what is your background in refrigeration?

  3. #3
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Moving a cold room

    Air Conditioning... Why?

  4. #4
    Join Date
    Jan 2009
    Location
    sunny norfolk
    Posts
    81
    Rep Power
    16

    Re: Moving a cold room

    if you have a suction rotolock valve, shut that down and with your receiver rotolock shut, pressure test the pipework, evaporator and your joints. once complete you can vac out then open both rotolocks

    if you have only one rotolock on the receiver then your compressor is holding your refrigerant back so i would reclaim it, pressure test, change filter, vac out, leak test and recharge the system

  5. #5
    Join Date
    Jan 2009
    Location
    sunny norfolk
    Posts
    81
    Rep Power
    16

    Re: Moving a cold room

    if your an ac engineer do you know anything about multi split systems (see my posted question on air con)

  6. #6
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Moving a cold room

    Thanks for the info Steve. I had a look at your Air con question it seems Yuri B has answered it for you.....

  7. #7
    Join Date
    May 2008
    Location
    poole
    Age
    38
    Posts
    17
    Rep Power
    0

    Re: Moving a cold room

    when i move a unit i recover all refrigerant into new reclaim bottle then once re installed i pressure test whole system so i know there are no leaks at all,then add the refrigerant back after carring out correct procedures,i have found a few times the valves leaking and pushing ofn to mix with the refrgerant,i just dont trust valves that have been in use

  8. #8
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Moving a cold room

    I was thinking that myself but just put the question out there to see what the general practice is. Sometimes valves do leak but if its a case of once in a blue moon you might be more inclined to chance your arm.

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Moving a cold room

    if the are magnetic valves,they can be hold open whit a static magnet (no electric), so the ofn can pass nicely. and no pressure can make them leak.

    Ice

Similar Threads

  1. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  2. Cold room floor
    By Andy AC in forum Commercial
    Replies: 8
    Last Post: 19-02-2009, 04:26 PM
  3. cold room
    By CHILLED4 in forum Trouble Shooting
    Replies: 5
    Last Post: 16-11-2007, 11:44 PM
  4. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •