    Wrong temp reading



    I have an Eliwell EWPC902T with a PTC probe. Actually 3 of them running different systems in identical setups. 2 are working perfectly. The third is giving me issues.

    The temperature reading starts out fine when a new probe is installed. Over the course of 24 hours the reading creeps higher. 24 hours = approx 1.5°C higher each day.

    As a result the temperature in the system gets lower and lower because the controller thinks it is too warm and keeps calling for more chilling.

    I have replaced the probe with a new one out of the box and it still gives a false reading. I have also connected a probe from a different system and the reading was accurate, although I have not left it on there for long.

    Would the controller be suspect here? It was used elsewhere some years ago, not sure of the exact history.

    Marine CHiller



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Wrong temp reading

    Swap the "suspect" Eliwell with one of the two "honest" ones. Then you know for sure fault is in the controller and not in some connection.

  3. #3
    Join Date
    May 2008
    Location
    Canada
    Posts
    30
    Rep Power
    0

    Re: Wrong temp reading

    I will try that. The other possible issue is that the probe is about 100m away from the controller. Anybody know the limit on distance between eliwell controller and ptc probe?

  4. #4
    Join Date
    May 2008
    Location
    Canada
    Posts
    30
    Rep Power
    0

    Re: Wrong temp reading

    Tried switching controllers. The issue still exists. So, in summary,
    1)the controller works perfect on the other systems
    2)two brand new probes gave the same result
    3)all connections have been re-wired

    My only theories
    1)100m with 4 connections (including ends) is too long of a run. Waiting on a reply from supplier for this answer OR on the wisdom of any of you here
    2)When the wire was run, it got damaged and wet/salty air is degrading it noticeably each day?!?!

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Wrong temp reading

    Extract from Eliwell handbook, link below...

    Fault signals - 'E1' = room sensor fault - check wiring & connections between control and sensor. If no fault in wiring, check sensor
    resistance value as per table shown below. 'E2' = evaporator sensor fault - check as per E1.
    Sensors - Eliwell controls predominantly use PTC sensors with NI100 & PT100 types also being used on some models.
    Sensors - connections - preferably use screw connection blocks or spade connections.

    Sensors - extension - PTC sensors are extendable to a max. of 100 mtrs using 1,5 mm square section conductor cable.
    Sensors - interference - avoid running sensor leads close to other electrical equipment and other cables conducting large switching loads. If this is unavoidable, use screened cable, earthed at both ends.

    Sensors - resistances - sensor temperature (degree C.) / ohms resistance

    Q1, Are you using the correct cable?

    Q2. Is it adjacent to power cabling?

    Handbook link..
    http://www.thermofrostcryo.co.uk/tec...ndbookv2.0.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Wrong temp reading

    i would solder all connections to the probe ,and use cable/wire that is at least twice the guage/size what are the other controllers probe lengths are they long ,if you are sure of the latter get crushed ice immerse probe into it should read 32/0 f/c,

  7. #7
    Join Date
    May 2008
    Location
    Canada
    Posts
    30
    Rep Power
    0

    Re: Wrong temp reading

    To Brian_UK:

    Q1, Are you using the correct cable?
    Using AWG 22 works out to .33 mm² section. Good call Brian. Oops.

    Q2. Is it adjacent to power cabling?
    It gets crossed by cable powering 10hp heat pump. Wire is also not shielded.

    Thanks for the handbook link.

    To cadwaladr:
    I like how you think. I have used the crushed ice method, also have a mercury thermometer to check against. Readings are definitely off.
    The other controllers have shorter cables (about 30m and 50m)
    Using larger cable is necessary according the Eliwell handbook - also good call.

    So, current plan:
    1)Replace cable with shielded 14 AWG
    and possibly
    2)Move controller closer

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Replies: 13
    Last Post: 10-05-2008, 04:22 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Replies: 9
    Last Post: 21-09-2007, 11:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •