    Reclaim



    If you remove all the refrigerant from a system ready to replace due to a leak (r407c) do you have to add oil aswell? As oil will have been removed from system during the reclaim.

    Thanks



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Reclaim

    if you had a leak on R407C or R410A,or sall i say ,a blend refrig, you to trow away the refrig and refill completely whit new. the oil on a hermetic is sufficient and do not have to add more.

    Ice

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Reclaim

    Only R407c was said to be replaced with a complete new refill.
    But according to Rhodia - largest French gas manufacturer - is even this no longer true. According to a press article, you simply may add R407c
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Reclaim

    If you reclaim with a recovery unit, then the oil stays in the system.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jul 2008
    Location
    london
    Posts
    102
    Rep Power
    16

    Re: Reclaim

    Even if I vac the system with the valves all open? Is this the same for all refrigerants? Whats signs will there be if it is low on oil? As is a sealed comp?

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Reclaim

    You vac pump or reclaim machine should not remove any oil from the system unless you have made a connection directly to the bottom of the oil sump.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Reclaim

    if you want to reclaim the refrig,make sure the recoverymachine is higher than the unit,so the oil gets a chance to flow back.

    and yes peter_1,i am aware of the article,we spoke of this before,but in doubt and the client is paying........i say no more.

    Ice

  8. #8
    Join Date
    Jan 2009
    Location
    sunny norfolk
    Posts
    81
    Rep Power
    16

    Re: Reclaim

    you could also start your vac from the receiver side so any oil that is foaming will stay in the system and not in the vac pump then open your suction side to double evac

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Reclaim

    so many ways and tools to recover refrig for a system, just make sure that you have an open loop,al valve's have to be open,so the refrig can pass.

    Ice

Similar Threads

  1. refrigerant reclaim
    By weidit in forum Air Conditioning
    Replies: 3
    Last Post: 25-05-2009, 07:38 PM
  2. Reclaim?
    By airflo in forum Air Conditioning
    Replies: 3
    Last Post: 03-09-2008, 11:24 AM
  3. Sporlan Heat Reclaim Valve
    By 750 Valve in forum Commercial
    Replies: 7
    Last Post: 05-07-2008, 03:20 PM
  4. Low head pressure Versus Heat reclaim.
    By taz24 in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 20-03-2008, 11:47 AM
  5. Reclaim units
    By ice-cream in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 14-11-2005, 08:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •