    Denco downflow



    Hi guys

    I have de-commissioned a denco downflow unit (removed gas) the system has had a leak. My question is
    If the unit was going to re- used somewhere else
    you would put virgin r407c in as the removed gas is now void! But if you where putting new gas in would you need to add oil? The compressor us sealed but it does say on use a certain type of oil?

    In what circumstances would you have to add oil?

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Denco downflow

    When you have had a major oil leak.

    I hope that you have put a holding charge in the unit to keep it dry.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    joshuatan's Avatar
    joshuatan Guest

    Re: Denco downflow

    If R407C gas is to be used the Mineral oil should be removed and POE oil used. You should be able to get the quantity from the compressor manufacturer and quote the model. Don't forget to stick a R407C sticker on the compressor with a date etc. I think you need to make sure the expansion is acceptable.

  4. #4
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    14

    Re: Denco downflow

    As the manufacturer of the equipment we do not recommend you carry out retrofits, it causes issues with compressors, evaporators (Glide) and also it has a knock on effect on the duty.

    Rob

  5. #5
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    223
    Rep Power
    17

    Re: Denco downflow

    Are you saying that you will be retrofitting an R22 system or that the system was always R407C and the original refrigerant charge is void because of fractionation?

    In a sealed system with no oil sight glass you should only put in the amount of oil that you take out, you dont know how much oil was in the refrigerant that you removed so I would'nt worry about it, assume that the vast majority of the original oil charge is still in the compressor.

    It doesn't sound that scientific but on smaller systems you have to take a few things for granted.

    Cheers
    Tutto il Mondo e un Paese

Similar Threads

  1. Denco & Danfoss info\training material
    By SteveDixey in forum Training
    Replies: 6
    Last Post: 06-06-2011, 10:12 PM
  2. Denco Close Control Units
    By Freecool in forum Air Conditioning
    Replies: 12
    Last Post: 05-05-2010, 12:50 PM
  3. Denco Johnson control
    By sparrow in forum Training
    Replies: 4
    Last Post: 13-04-2010, 10:26 AM
  4. Denco unit L.P trip
    By N.Lewis in forum Air Conditioning
    Replies: 9
    Last Post: 09-04-2010, 10:23 PM
  5. Denco Humidity Control
    By chimayblnd in forum Air Conditioning
    Replies: 2
    Last Post: 08-04-2010, 12:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •