    Question re: secondary refrigerant



    Does the salinity level of a brine solution used as secondary refrigerant in an ice plant, affect the freezing time of H2O to ice? Anyone who can shed light on this? Thanks in advance!



  2. #2
    Join Date
    Aug 2008
    Location
    Philippines
    Posts
    9
    Rep Power
    0

    Re: Question re: secondary refrigerant

    Quote Originally Posted by Ober View Post
    Does the salinity level of a brine solution used as secondary refrigerant in an ice plant, affect the freezing time of H2O to ice? Anyone who can shed light on this? Thanks in advance!

    I'm referring to the freezing time of the block ice.

  3. #3
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: Question re: secondary refrigerant

    B"H
    Ober,
    Any salt dissolved in water will depreciate freezing point. The higher the concentration of the salt in the brine the lower is the freezing point of the brine. Of course to freeze the brine to a lower temperature more energy needed to be with drowned and it will take a longer time. At 0% salt freezing point 32F, 5%salt freezing point @ 26.8F, 8% salt freezing point @ 23F

  4. #4
    Join Date
    Jan 2008
    Location
    West Coast British Columbia
    Age
    51
    Posts
    106
    Rep Power
    17

    Re: Question re: secondary refrigerant

    Hi Ober

    Let us consider the SP gravity of the secondary solution.
    As the strength or salt level is increased within the secondary solution a couple major things happen. the Specific Gravity increases causing pump capacity to drop and horse power required to increase.

    with this the solution also gains the ability to perform at a lower temperature.

    As long as your system can handle the increased pumping capacity and your coils can handle the increased TD across them.

    You should in theory be able to decrease you freezing time.

    Things to be aware of.

    Pump amperage will increase due to the increased SP.G

    Be aware of your compression ratio as you lower the suction pressure this ration is going to increase dramatically. To much compression ratio kills compressors.


    Here is a nice hand book on Calcium Chloride. which shows temp range by strength of brine.


    http://www.dow.com/PublishedLiteratu...romPage=GetDoc
    Refrigeration is not just cool, it is my life.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. need help on refrigerant question
    By fitzry1 in forum Training
    Replies: 0
    Last Post: 17-09-2008, 06:46 PM
  3. r134a question, calculating heat lost by refrigerant
    By kamikazi929 in forum Fundamentals
    Replies: 0
    Last Post: 03-01-2008, 08:19 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  5. Basic question about refrigerant to use
    By cbfull in forum Fundamentals
    Replies: 25
    Last Post: 07-08-2007, 02:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •