Thread: convert r134a to R-404a
24-05-2009, 05:55 PM #1
What would be involved in conerting a small stand alone freezer from R-134a to r-404a
28-05-2009, 05:18 PM #2
Re: convert r134a to R-404a
How much money you got!!! Having said that, the metering device, the dryer, maybe the compressor(depending on the manufacturer) will have to be changed, you may then have issues with capacity becasue the evap coil and cond coil is sized for 134a not 404A.
04-06-2009, 07:32 AM #3
I'm doing that right now on an old 3 door freezer that was R-12. The original compressor was a 3/4 HP. What I'm doing is replacing the complete condensing unit with 1 HP 404a that has a receiver. also getting rid of the cap tube. Replacing it with a TXV and a sight glass. Then I'll adjust the superheat as required. Another trick I've done many times is on an old R-12 walk in, I'll replace with a R-22 condensing unit, (same HP) and charge with HotShot to a clear sightglass and adjust the superheat as required. The compressor purrs and runs cool.
04-06-2009, 11:24 PM #4
05-06-2009, 01:50 AM #5
And sounds like R404A is up for the chop as well, due to high global warming factor.
magoo
08-06-2009, 01:20 AM #6
Hotshot is R-414b. It's used as a R-12 drop in replacement, the problem is with this and most R-12 drop in's is you can only charge to approx 80% due to head pressure problems. Not a good idea for compressor longevity. Also capacity is diminished. I've been using R-416a very successfully. Except it's not recommended on freezers or mineral oil applications. This whole refrigerant thing is like a "War on Refrigerants" the way government gets involved and passes these laws while the rest of us pay the price. ( So companies like Dupont can reap the monetary harvest) I've been doing service work on many types of projects for 30 years and saw the whole thing unravel. Nothing like Change You Can Believe In.
R507 in an R134a compressor: any danger?
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 21-12-2009, 01:44 AM -
R 404a
By Samarjit Sen in forum RefrigerantsReplies: 59Last Post: 07-08-2007, 06:35 PM -
Pressure Transmitter R134a Setpoints
By cooltrain in forum Technical SpeculationsReplies: 0Last Post: 28-02-2005, 10:05 AM -
Is there anything about R134a that is better than R12?
By dude in forum RefrigerantsReplies: 5Last Post: 01-03-2004, 10:59 PM
