    running 2 core sensor cable



    greetings gentleman
    advice required please... on a job running sensor cables eg supply air,ambient,return air, on coil, from a air con unit on a roof to a control panel in a plant room.
    I know your not supposed to run it with your mains cable how ever if you have no other way but to go the same route as your mains is run on cable tray to your control panel is there any serious inplications if you do it that way /long term?
    thank you in advance for your replys gentleman...



  2. #2
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: running 2 core sensor cable

    sensorman,

    you are right that sensor cable should not be run with power lines.Static,distortion and in accuracy in transmitting signals from sensor to electronic modules will result to errors.
    abet

  3. #3
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: running 2 core sensor cable

    If you use a good quality shielded cable you shoudn't have any problems.

    PP

  4. #4
    Join Date
    May 2008
    Location
    poole
    Age
    38
    Posts
    17
    Rep Power
    0

    Re: running 2 core sensor cable

    use screened cable,cost more but will do the job!

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: running 2 core sensor cable

    As they say, used screened cable but, please, only earth one end of the shield.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: running 2 core sensor cable

    Agree with pp, wandowski and Brian. Get the fully screened cable, the one with the woven screen around the leads.

  7. #7
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: running 2 core sensor cable

    Hi

    Don't know weather this is correct but i got told standard PTC or NTC probes can be run using any old cable up to 1000mtrs as they measure a very large resisitance between deg's.
    i've seen loads run in .75mm 3 core flex along side, wrapped around and on top of swa cables and never presented problems in years, they work fine.

    P.S. this is probes used on temp controllers for Lae, elliwel, etc, etc

    i'm not saying it's right, just what i've seen and been told

    CB

  8. #8
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: running 2 core sensor cable

    as others say, we use CY cable 1.5mm (not sure what cy stands for :-P)if long runs, with the screened earthed at one end only.

  9. #9
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: running 2 core sensor cable

    as chillyblue says i agree given maximum distance recommended by manufacturers,but have had the rare occasion where interference was giving problems.shielded is definitely the way to go.
    mmm to beer or not to beer...........lets drink breakfast

  10. #10
    Join Date
    Nov 2008
    Location
    Scotland
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: running 2 core sensor cable

    Quote Originally Posted by sensor man View Post
    greetings gentleman
    advice required please... on a job running sensor cables eg supply air,ambient,return air, on coil, from a air con unit on a roof to a control panel in a plant room.
    I know your not supposed to run it with your mains cable how ever if you have no other way but to go the same route as your mains is run on cable tray to your control panel is there any serious inplications if you do it that way /long term?
    thank you in advance for your replys gentleman...
    Hi

    I would use a screened cable with the screen earthed at on end. I use this for all my sensors, saves a lot af problems later.

    ice/runner

Similar Threads

  1. Problems with compressor running too cold
    By abrando1 in forum Trouble Shooting
    Replies: 8
    Last Post: 12-05-2009, 10:08 PM
  2. Core drill for rock
    By paul_h in forum Tools and Calculators
    Replies: 20
    Last Post: 17-05-2008, 12:47 AM
  3. Walkin cooler running to warm need help
    By The Butcher in forum Trouble Shooting
    Replies: 7
    Last Post: 03-08-2007, 09:19 PM
  4. Running Costs
    By Abe in forum Air Conditioning
    Replies: 4
    Last Post: 09-04-2007, 12:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •