    Smile Relay Overload Combination - how to install?



    Using a ohm meter my question is how do I figure the terminals..." run, common, start on a refrigeration compressor ?" I want to install an R041 relay/overload combination or maybe another Supco relay/overload to replace the factory oem parts on failed relay-overloads. thankyou God Bless



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Relay Overload Combination - how to install?

    Hi. Honestly, "R041", "Supco relay" does not say anything to me, as I do not work with them. Do I understand rightly, the working princip on you compressor is: neutral constant, live is "on" and "off", by that, there is a capacitor wired in the scheme? (and you wish the live to go through some ovelload protection?)

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Relay Overload Combination - how to install?

    But, in any case, and I have not yet seen otherwise, common-start is more Ohms than common-run.

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Relay Overload Combination - how to install?

    By that, start-run is still more, and includes the two above resistances.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Relay Overload Combination - how to install?

    if my memory is correct stat to run is twice the total of start to com
    start to com =5 ohms
    start to run= 10 ohms
    < the numbers arejust an egzample<
    can anyone confirm my memory?

  6. #6
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Relay Overload Combination - how to install?

    Resistance start / run is a sum of start/common + common/run. Resistance depends on the power of the motor, the more powerfull, the less (active) Ohms.

  7. #7
    Join Date
    Jan 2009
    Location
    jax, fl,
    Posts
    23
    Rep Power
    0

    Re: Relay Overload Combination - how to install?

    go to grainger or johnstone supply and pick up a 3in1 start kit for the compressor. take the model number and info off the label on the compressor and the counter sales guy or girl will give you what you need and the instuctions will help you identify the terminals on the compressor. also the compressor terminal cover has a diagrahm identifying the terminals.

  8. #8
    icehouse's Avatar
    icehouse Guest

    Re: Relay Overload Combination - how to install?

    This is a piece I wrote for a NATE certification prep course. And most times you read left to right : C S R
    FIRST:
    Single phase compressor motors have a "Start Winding" and a "Run Winding" with a "Common" connection between them. Therefore the total resistance is the sum of both windings.

    SECOND:
    Shorted motor windingsccur when the insulation on the windings become defective and allows a shorted condition (two wires to touch), allowing a bypass of the winding. Depending on how bad of a short it is possible for the compressor to operate, but will draw excessive amps.
    There should be no reading from any terminal to the compressor motor case using an ohmmeter.

    THIRD:
    Grounded motor windings occur when the insulation on the winding is broken down and becomes shorted to the compressor motor case.
    This can be verified with an ohmmeter by touching one lead to any terminal to the compressor motor case (it is recommended to scrape away paint).

    FOURTH:
    A compressor motor may have a weakened winding that will short to ground when called to run. It is therefore recommended that a "Hi-Pot" tester be used in conjunction with an ohmmeter to check for insulation failure.

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Relay Overload Combination - how to install?

    Quote Originally Posted by icehouse View Post
    It is therefore recommended that a "Hi-Pot" tester be used in conjunction with an ohmmeter to check for insulation failure.
    Somethimes also cald a "megger" device. the device send a small current over the windings so its possible to see or to find out whitch one is sort cutted.

    Ice

Similar Threads

  1. Overload protecter
    By ismayil59@yahoo in forum Electrical
    Replies: 24
    Last Post: 27-04-2009, 09:04 PM
  2. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  3. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM
  4. compressor relay
    By wilks in forum Electrical
    Replies: 2
    Last Post: 16-09-2007, 02:52 PM
  5. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 07:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •