    Manifold Gauge and Hose question



    Hi all,
    Just a quick question about gauges and hoses really,
    I work mainly on package units with the basic schrader valves (without service valves).
    Now I have just carried out my 2079 I am now required to test all the units for leaks every 6 months, I would like to carry out this by measuring and recording the superheat/subcooling, but every time I engage my hoses I am probably doing more harm than good!
    Now I am just wondering if there are any hoses out there that are specially designed to be put on and off these valves without loss of refigerant, for example with a longer end connection so it screws on far enough before it releases the valve so its sealed before releasing the refigerant.
    I currently use a red hose with a tap on the end and before attempting to take the hose off I close the tap and open my hi and low valve to rid whats left in the hose before removing.
    Any advice or help would be brilliant,
    Thanks Lee



  2. #2
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Manifold Gauge and Hose question

    Hi Lees,
    http://www.srw.co.uk/ do a set of hoses fitted with non return valves that`ll hold the refrigerant the line. Of course that means you`ll have to have a diferent manifold for each gas you deal with but that`s no bad thing as you`ll not have to purge the hoses each time you connect them.
    You`ll need to register with srw to view them but they do lots more stuff at good prices.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by lees8110 View Post
    Now I have just carried out my 2079 I am now required to test all the units for leaks every 6 months, I would like to carry out this by measuring and recording the superheat/subcooling, but every time I engage my hoses I am probably doing more harm than good!
    Yes, you probably are.

    You would be better off tracking evap delta-T. An increase in dT indicates airflow problems, while a decrease indicates refrigerant flow problems... or high humidity... or various other problems.

    If these are heat pumps, you would want to track the dT of the indoor coil in each mode, as the temp and volume of indoor airflow is relatively constant.

    Of course you would first need to establish a base dT for each unit in each mode (with everything functioning properly) to compare to.
    Last edited by Gary; 21-05-2009 at 09:50 PM.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Manifold Gauge and Hose question

    I see no sense at all in periodically testing for refrigerant charge problems. Why not instead periodically test for any and all problems?

  5. #5
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by Gary View Post
    I see no sense at all in periodically testing for refrigerant charge problems. Why not instead periodically test for any and all problems?
    Thankyou all for your advice and input so far I appreciate it, I am sorry for all the basic questions but am just keen to learn properly.

    What checks/precautions would you recommend for this aswell as what you have already suggested?

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Manifold Gauge and Hose question

    IMO gauges should only be connected to systems as a last resort, not on a maintenance/ leak check visit.

    As Gary says there are many ways to check if the system has a leak, firstly by carrying out a visual check of the system paying close attention to any signs of oil around joints, schraeders etc and maybe even using your leak sniffer.

    Other checks that need performing are,to verify the airflow through condenosr/evap are clear and are not full of dirt by checking the Delt T (air on/air off).
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Manifold Gauge and Hose question

    i am currently doing a nvq level 2 in ac and refigeration. i asked my tutor the other day about putting gauges on a system for maintenace. he said it is illegal to do so. you only put them on if you think the system is short of gas and as a last procedure really.

    is this true what he is telling me?

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Manifold Gauge and Hose question

    I don't think it is illegal but too many engineers think the first thing that should be done is put the gauges on when it isn't.

    Firstly it should be to check correct water/airflow through both coils, take temperatures and then if there is still a problem i would connect my gauges to check subcooling and then superheat.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  9. #9
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    82
    Rep Power
    18

    Re: Manifold Gauge and Hose question

    I always remember being told that gauges are diagnostic tool not maintenence tool.
    Nuff Said.
    "I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by moondawn View Post
    i am currently doing a nvq level 2 in ac and refigeration. i asked my tutor the other day about putting gauges on a system for maintenace. he said it is illegal to do so. you only put them on if you think the system is short of gas and as a last procedure really.

    is this true what he is telling me?

    If it is not, it should be!

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Manifold Gauge and Hose question

    If it is not, it should be!


    Oh dear... will a logo have to change?

  12. #12
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by desA View Post


    Oh dear... will a logo have to change?


    no cos that engineer is on a call to a unit showing signs of Short of gas

  13. #13
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Manifold Gauge and Hose question

    If the condenser coil is accessible, measure the temperature at the end of the coil, work your way down from the top and you should see a decrease in temperature, when you start to see no change in temperature that reading will be your saturated condensing temperature, subtract the liquid line temperature and you will have the subcooling value.

    Cheers
    Tutto il Mondo e un Paese

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Manifold Gauge and Hose question

    You only have to check your system for leaks according to EN378, and it's not illegal to put your gauges on a system.
    Why not use these
    I have 2 (1/4" and 5/16 " SAE) in each toolcase, it's a standard tool I use since years.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by El Padre View Post
    If the condenser coil is accessible, measure the temperature at the end of the coil, work your way down from the top and you should see a decrease in temperature, when you start to see no change in temperature that reading will be your saturated condensing temperature, subtract the liquid line temperature and you will have the subcooling value.

    Cheers
    Cheers for this Would this apply to the evapourater too?

  16. #16
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by Peter_1 View Post
    You only have to check your system for leaks according to EN378, and it's not illegal to put your gauges on a system.
    Why not use these
    I have 2 (1/4" and 5/16 " SAE) in each toolcase, it's a standard tool I use since years.
    Peter this is what im looking for, were would I find myself a set of these?

    Cheers Lee

  17. #17
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by lees8110 View Post
    Cheers for this Would this apply to the evapourater too?
    I used the subcooling example as it would be very rare on AC systems to have access to the evaporator coil, because you are looking for the end of the latent heat gain the same principle would apply for superheat, on Daikin splits for example you can see the coil sensor values via the controller (setting code 41).
    Gary makes a great point regarding checking air/water flow prior to anything, I have been caught out several times, especially on water chillers in the past.

    Cheers
    Tutto il Mondo e un Paese

  18. #18
    Join Date
    Sep 2006
    Location
    england
    Posts
    285
    Rep Power
    18

    Re: Manifold Gauge and Hose question

    your location is manchester you have dean and wood +ryan aircon ref spares on your doorstep

  19. #19
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Manifold Gauge and Hose question

    I heard Ryan Air Con Spares had moved/closed and was concentrating on internet orders instead?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  20. #20
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: Manifold Gauge and Hose question

    check with heatcraft,,,,australia there have some fittings u cn use on the schrader valve ...

  21. #21
    pipeman's Avatar
    pipeman Guest

    Re: Manifold Gauge and Hose question

    Quote Originally Posted by marc5180 View Post
    I heard Ryan Air Con Spares had moved/closed and was concentrating on internet orders instead?
    They still have a trade counter, its in Irlam. About a mile or two down the road from macro

Similar Threads

  1. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM
  2. URGENT: Evacuation setup :(
    By swampthing in forum Fundamentals
    Replies: 38
    Last Post: 23-06-2008, 03:53 AM
  3. CPS Manifold gauge ports
    By JD-SMART-REPAIR in forum Trouble Shooting
    Replies: 27
    Last Post: 15-06-2008, 06:55 PM
  4. Diagnosing reversing valve vs scroll compressor?
    By Larry2 in forum Technical Discussions
    Replies: 16