    How do I design & calculation with long refrigerant pipe line?



    Hi.... All Refrigeration man !

    I'm designing that the Cascade Refrigeration freezer for shrimp cook ( R-23 Low stage , R-404 High Stage) , and now I have some problem that the too long of liquid & suction R-23 pipe line ( about 100 m.) , we use 3/4" liquid line (-20 c ) , 1.5/8" suction line , the both of them applied K type copper tube. , after we installation of system we found the compressor can not be start ( High Pressure cut off ) and I thing that the cause of very long pipe line( make the vaporize of R-23 to Hight pressure )
    How do I know or basic calculation about compressor power ( motor hose power )that can operate and starting.?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How do I design & calculation with long refrigerant pipe line?

    What is mass flow thru lines?
    Did you considered instalation of liquid refrigerant pump?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: How do I design & calculation with long refrigerant pipe line?

    If this is a cascade system with long pipe lines you could also have an issue with the refrigerant charge being increased and forcing you to install a larger fade-out vessel (expansion vessel for the low temp part of the system). The cascade refrigerant needs some additional volume to expand to reduce the pressure in the low temp system.

    You have not provided very much detail to say why the compressor does not start though....
    If all else fails, ask for help.


  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: How do I design & calculation with long refrigerant pipe line?

    How did you charge the system?

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: How do I design & calculation with long refrigerant pipe line?

    BASICREFRIGERANT LINE SIZE CALCULATOR PROGRAM IS AVAILABLE IN SOLKEN 6.0 VERSION . MIGHT BE OF HELP. LET ME KNOW IF THIS COULD BE OF HELP . contact me on ddk0123@gmail.com

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: How do I design & calculation with long refrigerant pipe line?

    its not only the lenght of the pipes,but the way of expantion to considder. also the volume of the refrig vessel and the houskeeping / return of the oil.i think he is better of whit heatexanchers in liquid pump. the liquid it self can be a brine mixture for his specific temperatures.

    Ice

Similar Threads

  1. Single room a/c - long pipe run?
    By electro in forum Air Conditioning
    Replies: 7
    Last Post: 07-08-2006, 09:49 PM
  2. Calculation of "U" in Evaporator design
    By anup in forum Fundamentals
    Replies: 4
    Last Post: 03-11-2005, 04:55 AM
  3. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM
  4. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •