    Daikin Inverter board failures



    Just wondered if any of you guys out there have had any problems with Daikin VRV inverter boards failures latey - VRVII or III.

    Recently we changed a board and a compressor on an REYQ8M8W1B unit (U2 fault) and 1 day later after a rain show another Inverter board went on a different unit on the same site (RXYQ18P7W1B).
    When removing the old board our engineer noticed what looked like water marks on the back of the Inverter board heat sink. The latest one to go has the same water marks.
    According to our engineer it looks like water is seeping in around the condenser fan bracket which is attached above the Inv board box.

    To make matters worse it appears to be std proceedure to change the compressor with the inverter board. Crazy if there's nothing wrong with the comp - the subject of an earlier thread.

    Now this may be coincidence but I'm not so sure. If water ingress is the reason for the board failure then there should be no need to change the compressor. More to the point is this not a manufacturing / warranty issue. Anyone else out there with anything similar?


    If in doubt read the instructions. If still in doubt follow them.

  2. #2
    Join Date
    Aug 2008
    Location
    Belgium
    Age
    44
    Posts
    74
    Rep Power
    16

    Re: Daikin Inverter board failures

    Now that I have seen this thread, I think I need to investigate something on a RZQ250 (skyAir) unit that needed a new inverterboard. I still have the faulty one at the office. I'll check that out and see if it also has water traces.

  3. #3
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    82
    Rep Power
    18

    Re: Daikin Inverter board failures

    I have not had the water damaged board problems myself, but I would always recommend changing the comp' after an inverter PCB failure. Although the comp' may check out OK, who is to say it won't start to suffer insulation breakdown of the windings, maybe after extended run times or high frquency operation.
    If it's a warranty inverter PCB failure, Daikin will usually insist the comp is changed, and give you one under warranty, therefore when its out of warranty we always change them as a pair. If you don't & the PCB fails again, it starts a whole chain of arguments about whose fault it is, and it all gets kinds messy!!



    Just my 2 penneth!
    "I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."

  4. #4
    Join Date
    Apr 2009
    Location
    aberdeen
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: Daikin Inverter board failures

    Hi there, just been reading up on your VRV11&111 invertor board problems. Firstly i have not found any problems with water damage to any boards and would recomend changing the compressor after each invertor board failure, saves any hassle.
    Secondly i would look into any transportation damage or installation movement incase of movement of panels etc. Anyone with any ideas.

  5. #5
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin Inverter board failures

    Hi everyone it's an interesting thread...
    I had inverter board failure on VRV II and III due to rain water passing on the top it...
    Anyway it's possible to test the board in mode 2 code 28 - disconnect the inverter comp first -.
    Also the AC voltage on U/V/W while running is about 190 VAC under 52 HZ to reach 390 VAC under 210 HZ, - except for 8 HP= 266 HZ - .
    Soon i'll change an inverter comp due to abnormal noise on VRV II then i'll check the comp on usual power supply under 400 VAC 50HZ, while the comp is outside of course, this could be helpful to check the current passing the coils out of refrigerant charge...
    rgds
    cool#9

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Daikin Inverter board failures

    Hi Guys. Here’s an update to this story.
    Even though it was in warranty we took a chance (gut feel) and only changed the board on the 2nd inverter board failure. As it turned out the compressor was fine (phew) and it took 2hrs instead of the 2 days it would have taken if we had had changed the compressor as well (reclaim gas / replace comp / vac –out / pressure test / recharge / re-commission). We also had a Daikin field engineer come out to witness the changeover, inspect the boards and the installation generally.
    He agreed there appears to be water damage on both Inverter boards which might be caused by the suction effect of the outdoor fan drawing water into the inverter board panel. He’s off to check with Daikin Europe for any other known reports &/or fixes. Question is why are these boards suddenly going now on systems that have been in and working for 2-3 years? It’s not as if we’ve had no rain for that time!
    More to the point what’s stopping the same problem happening again to the new boards?
    Until I hear back from Daikin I would suggest you guys check any inverter board failures / U2 faults (vertical discharge fan VRVII & III 2-pipe & 3-pipe) for evidence of water damage before electing to change the compressors as well. The difference in cost to a customer for a board only vs a comp & board is considerable.
    If I get any more news I will update this post.
    If in doubt read the instructions. If still in doubt follow them.

  7. #7
    Join Date
    Oct 2008
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Daikin Inverter board failures

    I’ve been seeing a lot of complaints in the threads about inverter board failing. This are becoming the common mishaps when dealing with inverter systems due to the sensitivity of its electronics. I'm from a tropical country and it doesn't sound promising that this happens often. Please do keep us updated with your troubles.

  8. #8
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Daikin Inverter board failures

    Quote Originally Posted by wingman View Post
    Now that I have seen this thread, I think I need to investigate something on a RZQ250 (skyAir) unit that needed a new inverterboard. I still have the faulty one at the office. I'll check that out and see if it also has water traces.
    Me too on an REYQ10 , engineer changed the pcb not compressor as it checked out OK but 2nd board blew right away!!! so although it may not have been water ingress I will be looking into this. The real problem I find is telling the Customer that both have to be changed and then telling him the cost!

  9. #9
    Join Date
    Aug 2008
    Location
    Belgium
    Age
    44
    Posts
    74
    Rep Power
    16

    Re: Daikin Inverter board failures

    Quote Originally Posted by yinmorrison View Post
    Me too on an REYQ10 , engineer changed the pcb not compressor as it checked out OK but 2nd board blew right away!!! so although it may not have been water ingress I will be looking into this. The real problem I find is telling the Customer that both have to be changed and then telling him the cost!
    2 boards ? ... Oh jeez. Prepare yourself with a defibrilator.

  10. #10
    Join Date
    May 2009
    Location
    uk
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Daikin Inverter board failures

    hi all if your invertor boards are blowing straighta away also check your fan capacitors as these cause the inverters to blow ( with some bang). and you do have to change both as faulty invertor board can nakker up the compressor and vice versa.....

  11. #11
    Join Date
    May 2009
    Location
    uk
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Daikin Inverter board failures

    balls my fault main board on vrv multisplits that happens to .... i never read the thread properly

Similar Threads

  1. daikin L0 inverter problem
    By robin r33 gtr in forum Air Conditioning
    Replies: 17
    Last Post: 11-03-2010, 11:25 PM
  2. Daikin Inverter Board / Compressor issues
    By Greengrocer in forum Air Conditioning
    Replies: 12
    Last Post: 21-04-2009, 10:12 PM
  3. Daikin VRV wiring adapter board
    By mchild in forum Air Conditioning
    Replies: 6
    Last Post: 24-11-2008, 11:02 AM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. Inverter systems
    By Latte in forum The Trail of Tears
    Replies: 23
    Last Post: 11-07-2007, 12:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •