    Hello, I would like to check with you guys what is the proper method of calculating the capacity of an air-con unit. Please see below for the 2 different methods that I would like to check on, and the source that I obtained the calculations from.
    Source: Internet conversion table :
    1 Ton = 12000 BTU/h = 4.72 Horsepower = 3.52 kW
    Source: A few aircon servicing/repair companies
    1 Ton = 12000 BTU/h = 1.33 Horsepower = 0.99 kW
    Which is correct? Thanks
    11,025
    Re: Capacity Conversion Table
    The first one is correct.
    If you need a universal converter then please try this one...
    http://www.katmarsoftware.com/uconeer.htm
    Split Croatia
    6,151
    Second one is probably comparison from compressor refrigerant capacity to motor power consumed by compressor!