    Smile Louvers on Evaporators



    Has any one seen anything like this:-

    I have a coldroom-with a pitched roof. The evaporators are located at the bottom of the pitch as it were. They have louvers front and back which close on defrost for some reason! has anyone ever heard of this before!

    Because of the louvers fitted to standard evaps we are having problems, airflow related i think, maintaining temperature. I would like to get rid of them. Does any one know any reason why not >?


    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Louvers on Evaporators

    Do you perhaps have a picture?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Louvers on Evaporators

    These are probably very old. The louvers are supposed to close during defrost so that the coil can be cleared quickly. Supposedly, the dampers also reduce the amount of heat/water that could leave the coil during defrost.

    Seems like a lot of excess contraptions to just defrost a coil.

    Was the room ever able to maintain temperature, or was this something that just started?
    If all else fails, ask for help.


  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Louvers on Evaporators

    I had seen such things. It must be very old installation. The basic reason was to maximise defrost effect by closing the louvers at the time of defrost. Infact Thermoking truck refer units has similar systems even now a days. But actually closing / opening louvers becomes more problematic over a period of time.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Louvers on Evaporators

    the solution could be to disconect the louvers leave them fully open and fit a hold off stat, so when the unit has finished a de-frost the new stat holds off the evap fans untill the evap gets down to 0c or -5c whatever you think apropreate for the job,the stats sensor to be inside the evap casing

  6. #6
    Join Date
    Mar 2009
    Location
    Oregon Coast
    Posts
    56
    Rep Power
    16

    Re: Louvers on Evaporators

    I have had to change some of these types in the past. I remove the lovers and put a time delay on the fan motors. The louvers will reduce the air flow and cause a cavitation that disturbs the air flow causing some amount of air to short circuit.

  7. #7
    Join Date
    Jun 2004
    Location
    Wirral UK
    Age
    58
    Posts
    68
    Rep Power
    20

    Re: Louvers on Evaporators

    The problem is that this freezer must stay below -21 . It does usually below the evaporators but not above due to little or no air movement and lights generating heat . There are two rooms back to back with and apex roof. So each room has half of the apex. So a high wall and a low wall with a slanted roof.

    The Evaporators are located on the low wall. The room actually just about maintains temperature. Each room has two evaporators capable of 100% of the duty. Run in Duty and Standby.

    The room is around 3-5 years old. The evaporators are modern Techniblock 1000 A4523 fan evaps- the louvers are an add-ons. The condensing units have the same model number!?!

    The issue is that we feel the louvers are hindering the operation of the room by directing the airflow in a straight line and reducing the circulation effect from the fans. I would like to remove to louvers but, I need to be sure that the is no advantage to keeping them.

    Yes they close on defrost, but does that make them work better or keep th room cooler or make them more efficient. Is this just the folly of a mis-guided designer who got carried away with theories of no substance?

    Your thoughts gentlemen please!
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"

Similar Threads

  1. 1 Tev 2 Evaporators
    By Renato RR in forum Technical Discussions
    Replies: 14
    Last Post: 18-11-2009, 02:58 PM
  2. Flooded & Pump Evaporators
    By MrReds in forum Fundamentals
    Replies: 3
    Last Post: 24-01-2007, 10:11 PM
  3. Flooded & Pump Evaporators
    By MrReds in forum Fundamentals
    Replies: 2
    Last Post: 24-01-2007, 06:29 PM
  4. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  5. Evaporators: Stainless Steel or Galvanized S.
    By Friobernal in forum Technical Discussions
    Replies: 2
    Last Post: 28-10-2002, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •