    Unhappy problem TXV walk in cooler



    hello i am from P.R , last day i replacement a condenser unit tecusem 3/4 HP, Refrigerant 409, 115 volt, 11.6 amp. and replecement to a thermostatic expancion valve using 1/2 hp emerson for R-409.

    in this moment stay whit parameter ( HI press= 185 psig, LOW press= 20psig, AMP= 12.0, siglass still bubble, the evaporator star frost the firt line the coil and the rest is wet, ok and now is the mistery the expancion valve using external equalizer and look frost to injecting liquid to de suction line but the coil never to flood i not have idea what happenig i never see the external equalizer fort before flood the evap coil if somebody help me appreciate thank



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: problem TXV walk in cooler

    Did you replace the filter/drier?

    What is the walk-in temperature (temperature of the air entering the evaporator)?
    Last edited by Gary; 28-05-2009 at 06:59 PM.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: problem TXV walk in cooler

    Is the TXV sensing bulb mounted upstream from the equalizer line?

  4. #4
    Join Date
    Jan 2009
    Location
    jax, fl,
    Posts
    23
    Rep Power
    0

    Re: problem TXV walk in cooler

    sounds like the valve is starving. open it up 1 full turn counter clockwise. do you know how to check and set the evaporator superheat? if not google superheat. 10 degrees of superheat is ok for a walk in cooler.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: problem TXV walk in cooler

    Quote Originally Posted by hd88 View Post
    sounds like the valve is starving. open it up 1 full turn counter clockwise. do you know how to check and set the evaporator superheat? if not google superheat. 10 degrees of superheat is ok for a walk in cooler.
    At this point there is no reason to believe that the valve needs to be adjusted.

Similar Threads

  1. Walk in refer dual coil problem any ideas????
    By Supertech87 in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 07-06-2009, 06:37 AM
  2. 134A reach in cooler problem
    By bvis in forum Trouble Shooting
    Replies: 11
    Last Post: 16-03-2009, 02:36 AM
  3. walk in cooler evaperator keeps freezing up
    By ewart in forum Trouble Shooting
    Replies: 21
    Last Post: 30-07-2007, 09:30 PM
  4. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM
  5. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •