Filter dryer question.
Hi guys,
recently (read last october2008) I was asked to do service on a MTA chiller unit.
I noted that there was a refrigerant leak in the evaporator and the unit needed repair. After long discussions who was going to pay for the repair, 5 other techs detected the same thing.
Now we are may and still nothing is done. (long story though so I am skipping the rest) In the meantime two other companies have seen the unit claiming there is no leak in the unit. One company claimed the filter dryers have never been replaced. Something they claim that has to be done every 3 years.
According to what I know, once you start up a system you do not touch the filter dryer unless ofcourse you had to change something on the refrigerant system. Or whenever you have done an oil change (when the oil is acidic or marginal of quality)
Can someone either confirm or deny this, if it is indeed neccesary to change out FD's after 3 years if nothing is wrong with system.Last edited by wingman; 19-05-2009 at 10:17 PM.
-
19-05-2009, 11:42 PM #2
Re: Filter dryer question.
That's a hard one to be specific on Wingman.
If the compressor operates at high compression ratios, for whatever reason, then system oils and refrigerants can break down and begin the onset of internal damage.
It might, therefore, be argued that the filter/drier may be approaching overload and should be replaced to maintain system cleanliness.
A case study by Sporlan some years back may be of interest.
http://sporlan.jandrewschoen.com/40-176.htmBrian - Newton Abbot, Devon, UK
Retired March 2015
-
20-05-2009, 06:46 PM #3
Re: Filter dryer question.
From my experience, I would change a filter \ dryer on two events:
1. The system was open for any reason.
2. Temperature difference between inlet and outlet of
the dryer. [ 2°C indicate a partial blockage]
-
21-05-2009, 02:52 PM #4
Re: Filter dryer question.
Brian,
the system runs under normal conditions, so no high condensation temperatures.
Chemi cool,
Just as I would do, I would not change a filter unless the system has been opened for a reason or when I have a temperature difference between inlet or outlet.
Thanks for the answers guys, realy appreciated
Similar Threads
-
extra expansion valve and dryer port
By CoolWell in forum FundamentalsReplies: 8Last Post: 07-10-2008, 03:10 AM -
Removing sweat on Filter Dryer dangers?
By mooka in forum DomesticReplies: 16Last Post: 09-10-2007, 05:09 PM -
Scroll compressor with TXV no Receiver no filter Dryer
By FCS in forum FundamentalsReplies: 7Last Post: 19-06-2007, 10:51 PM -
questions in the method of testing filter filtration capability
By jasonsun in forum Technical DiscussionsReplies: 0Last Post: 10-05-2007, 04:45 AM -
Urgent, Kirchoff question
By Peter_1 in forum FundamentalsReplies: 4Last Post: 20-01-2004, 03:12 PM