Results 1 to 9 of 9
  1. #1
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Low-voltage protection



    We seem to have a number of occurrences of major voltage reduction, over extended periods.

    An example was a period of at least 10 hours where line voltage measured at 187V, against the standard delivery of 220V.

    The aircon systems (single phase) in my home couldn't even muster enough muscle to turn the evap fan properly, let alone the compressor.

    I am looking for a cost-effective, simple way to shut down a heat-pump, or aircon system, when line voltage goes below an acceptable threshold & then either auto-set when it returns to the acceptable value, or have to be manually reset.

    Thanks so much for your input.



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Low-voltage protection

    Hello. There are protective relays sensing voltage between neutral and each phase. Thera are two potentiometers on them with which you set the lower limit (let's say 210V) und the upper one. It has outputs - and I would feed through them a powerful contactor which would cut power to critical to undervoltage appliances. This is what first came to my mind. Such relay are rather expensive. Don not remember the name with which worked just recently.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Low-voltage protection

    Thanks, Yuri.

    Apologies - I should have added - its a single phase compressor, with low-load amps at around 6A & top-end amps at around 11A.

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Low-voltage protection

    pretty sure phasefale have one for single phase 240 volt 50 hz,your voltage & or hertz being different,one would think they have an application to suit.happy hunting
    mmm to beer or not to beer...........lets drink breakfast

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Low-voltage protection

    ^ Thanks very much, 'lowcool'.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Low-voltage protection

    Check page 9 here!

    Model RM17 UBE 15

    Must be used with contactor or power relay

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Low-voltage protection

    I have a brother who lives in Spain where line voltage varies considerably, often affected by the neighbour turning on the kettle!!

    Since I sent himover one of these
    http://www.apc.com/products/family/index.cfm?id=67
    his problems have been much reduced.

    From memory, I think this model adjusts for variations between 135V and 290V, giving out a constant 230V, although it's been some time since I read the spec sheet.

    Have a good look around the APC web site - I'm sure you will find something that 'fit's the bill'

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Low-voltage protection

    Quote Originally Posted by frank View Post
    I have a brother who lives in Spain where line voltage varies considerably, often affected by the neighbour turning on the kettle!!

    Since I sent himover one of these
    http://www.apc.com/products/family/index.cfm?id=67
    his problems have been much reduced.

    From memory, I think this model adjusts for variations between 135V and 290V, giving out a constant 230V, although it's been some time since I read the spec sheet.

    Have a good look around the APC web site - I'm sure you will find something that 'fit's the bill'
    Is his unit inverter type?

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Low-voltage protection

    Yes it is, but his fridge, microwave, tv etc isn't.

    if you purchase the correct size or multiple units, you can supply different pieces of equipment separately.

Similar Threads

  1. Panasonic inverter -Power factor protection
    By Blackbird in forum Air Conditioning
    Replies: 3
    Last Post: 28-06-2008, 01:17 PM
  2. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 06:11 PM
  3. capacitor comparison
    By jaison in forum Trouble Shooting
    Replies: 6
    Last Post: 21-03-2007, 10:42 PM
  4. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 08:55 PM
  5. Compressor Check for locked rotor voltage
    By shogun7 in forum Trouble Shooting
    Replies: 0
    Last Post: 04-04-2004, 12:44 AM