    Pressure test pressure?



    When pressure/leak testing a system, what pressure should you charge the system to with nitrogen and what precautions should be taken in regards to pressure controls and other devices?



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Pressure test pressure?

    yo M8, always test on 1,1 times the maximum operating pressure given by the brand.

    Ice

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Pressure test pressure?

    Quote Originally Posted by 440hardtop View Post
    When pressure/leak testing a system, what precautions should be taken in regards to pressure controls and other devices?
    look up the manual for by-passing the valves,or opening them on the main board.
    it depends on the brand you are working on.

    Ice

  4. #4
    Join Date
    Sep 2005
    Location
    UK
    Posts
    33
    Rep Power
    0

    Re: Pressure test pressure?

    Hi guys
    I normally test VRF & Splits to 300psi/20bar, tap the guages & take a picture of the dials. When presure testing Chillers & other plant fitted with Safety Valves I check what the valves are set at & test to 20psi less than set presure. I've found that Safety valves, once blown, frequently will not reseat properly. I also find that it's worth looking for one way check valves on chillers with Screw Compressors as the check valves can prevent one from venting all the OFN resulting in NCG's in the system.
    Regards
    Frostycold

  5. #5
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Pressure test pressure?

    You need to look at MWP of sytem normally 2 different values for high and low side. Then remove all PRVs and blank them off. Pressurise to 1.3 times MWP for strength test. The reduce the pressure for leak test to 1 or 1.1 times MWP. this is a good time to set your pressure trips . Then reduce back to zero and refit PRV's. This is a highly dangerous operation and the system should not be left during this operation. The other way is to look at your comparitor for the refrigerant and find the maximum design temp and pressure test to 1.3 times this pressure temp relationship.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure test pressure?


  7. #7
    olelogolie's Avatar
    olelogolie Guest

    Re: Pressure test pressure?

    I would like to get information and all specification of the VRV Systems

    Thanks and regards.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pressure test pressure?

    Go to manufacturers websites.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Pressure test pressure?

    Hi 440,

    The guidelines here are High side = 55 Deg (Air cooled) 43 Deg (Water cooled) and Low side= 32 Deg, Strength test would be *1.3 pressure leak test * 1.1, it goes without saying to know the max pressures of each component in the system, as mentioned previously.

    Just noticed the original post was in 2009, good luck with the Ashes!

    Cheers
    Tutto il Mondo e un Paese

  10. #10
    ashraf Bhatti's Avatar
    ashraf Bhatti Guest

    Re: Pressure test pressure?

    what is standar valeu of supper heat & sub cooling in HVAC system desigened for pharma grade?

  11. #11
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Pressure test pressure?

    For the OP, be careful with chillers! Evaps often have a relatively low MWP. Chuck in 30Bar & you may well burst the gaskets, flooding the refrigeration circuit.
    Trane's rule of thumb for leak testing was start with 10Bar. You'd be surprised - almost every leak showed up at that pressure. A very few times we went to 12Bar to find real pinholes. But their evaps are only PT'd to 14Bar, so we never went beyond 12Bar, just to be safe.

  12. #12
    Join Date
    Nov 2010
    Location
    between the compressor and PC
    Posts
    25
    Rep Power
    0

    Re: Pressure test pressure?

    Ok I'm confused here... If the high side normal working pressure for R400's and R500's is anything up to 15bar what pressure should we test to for strength and leak testing? Isn't this governed by code in the USA? I though it was twice the normal working pressure?? but heck I'm new..

  13. #13
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    208
    Rep Power
    16

    Re: Pressure test pressure?

    Check the Standards for your country, but all normal test figures are given in the posts above.

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •