Results 1 to 6 of 6
-
18-05-2009, 06:20 PM #1
30 gx chiller prodialog plus phase-3
hi,
any body knows what is the normal winding tempreture of the 06na compressor(carrier) one compressor is overheating.motor cooling valve is ok.pls help
-
18-05-2009, 07:23 PM #2
Re: 30 gx chiller prodialog plus phase-3
How do you know that compressor is overheating, what are the symptoms?
Last edited by Brian_UK; 18-05-2009 at 11:02 PM. Reason: Spelling...
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
18-05-2009, 10:50 PM #3
Re: 30 gx chiller prodialog plus phase-3
did you check the running Amps of each winding???
check the front-right site,were the oil sight glass is,it has to be cold there,and hot more to the left on the same place.
check the subcooling.
Ice
-
19-05-2009, 06:43 PM #4
Re: 30 gx chiller prodialog plus phase-3
hi,
thanks for the reply. actualy the cooling valve had the problem. (sv coil ok but mechanisam was stuck position) winding tem was 95c
any set point is there for cooling valve or economiser valve?
Is it always on when the compressor is on?
-
19-05-2009, 08:07 PM #5
Re: 30 gx chiller prodialog plus phase-3
I believe, Carrier chillers do not have settable temp for motor winding cooling (probably, no one chiller, or other type of refr equipment has, being pre-programmed and out of reach). Cooling solenoid seems to operate periodically, by impulses from the main processor.
-
26-05-2009, 01:38 PM #6
Re: 30 gx chiller prodialog plus phase-3
Normally the motor temperature is around 85 C. Just for future reference, beside the terminal pins is a spare temperature sensor for the windings in case the original goes out of range. If you change it make sure you connect onto the right connection.
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Absorption Chiller VS Mech. Chiller
By Intern in forum IndustrialReplies: 20Last Post: 30-05-2009, 08:31 AM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM