    30 gx chiller prodialog plus phase-3



    hi,

    any body knows what is the normal winding tempreture of the 06na compressor(carrier) one compressor is overheating.motor cooling valve is ok.pls help



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 30 gx chiller prodialog plus phase-3

    How do you know that compressor is overheating, what are the symptoms?
    Last edited by Brian_UK; 18-05-2009 at 11:02 PM. Reason: Spelling...
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: 30 gx chiller prodialog plus phase-3

    did you check the running Amps of each winding???
    check the front-right site,were the oil sight glass is,it has to be cold there,and hot more to the left on the same place.
    check the subcooling.

    Ice

  4. #4
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: 30 gx chiller prodialog plus phase-3

    hi,

    thanks for the reply. actualy the cooling valve had the problem. (sv coil ok but mechanisam was stuck position) winding tem was 95c

    any set point is there for cooling valve or economiser valve?

    Is it always on when the compressor is on?

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: 30 gx chiller prodialog plus phase-3

    I believe, Carrier chillers do not have settable temp for motor winding cooling (probably, no one chiller, or other type of refr equipment has, being pre-programmed and out of reach). Cooling solenoid seems to operate periodically, by impulses from the main processor.

  6. #6
    Join Date
    Nov 2005
    Location
    Ireland
    Posts
    23
    Rep Power
    0

    Re: 30 gx chiller prodialog plus phase-3

    Normally the motor temperature is around 85 C. Just for future reference, beside the terminal pins is a spare temperature sensor for the windings in case the original goes out of range. If you change it make sure you connect onto the right connection.

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  3. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Replies: 7
    Last Post: 13-12-2008, 03:43 PM
  4. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  5. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •