length of each coil’s refrigerant circuits
Hello,you guys!
In the evaporator or condenser, how to design the length of each circuit? It's the same that how many circuits we may design.
As we know, it's quite difficult to calculate the refrigerant pressure drop through the tube. So it's not easy to design the circuit according to the pressure drop. But I think there is some rule of thumb about the length. It may come from the engineers' experience.
Thank you!
Wilson
-
18-05-2009, 03:08 PM #2
-
18-05-2009, 03:22 PM #3
-
19-05-2009, 03:56 AM #4
Re: length of each coil’s refrigerant circuits
There is no rule of thumb, it comes back to effective surface area and heat transfer per circuit. Added complication is pressure drop per circuit. Small coils single circuit, large coils multi-circuit, whether condensers or evaporators.
Remove rule of thumb from your vocabulary. Calculate!!!!.
Rule of thumb is in the same league as "assume " and assume translates to Ass-u&-me.
magooLast edited by Magoo; 19-05-2009 at 03:58 AM.
-
19-05-2009, 04:22 AM #5
Re: length of each coil’s refrigerant circuits
Originally Posted by Magoo
Coil circuiting is a lengthy discussion full of specifics I am not prepared to get into, so I will bow out gracefully.If all else fails, ask for help.
-
19-05-2009, 04:39 AM #6
Re: length of each coil’s refrigerant circuits
Thanks,Magoo!
Yes, rule of thumb is not good,but it can guide us. As it's quite difficult to calculate the pressure drop of the two phase refrigerant flow, if we use the macro way to calculate, it may not be correct or accurate.
But if use the micro way, like using CFD to simulate the flow, it would be too difficult and time-consuming.
And if there is some experience, we will know the suitable range for the tube length, at least we can check whether our calculations falls into the range or not.
I suppose that we may use the suitable gas refrigerant velocity to determine the number of circuits.
-
19-05-2009, 04:44 AM #7
-
19-05-2009, 06:28 AM #8
Re: length of each coil’s refrigerant circuits
It was a rule of thumb
We take a max circuit length of 30 mIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
20-05-2009, 04:00 AM #9
Re: length of each coil’s refrigerant circuits
Peter_1, is it 30 meter too long?
-
20-05-2009, 06:02 AM #10
Re: length of each coil’s refrigerant circuits
But if use the micro way, like using CFD to simulate the flow, it would be too difficult and time-consuming.
-
20-05-2009, 06:53 AM #11
Re: length of each coil’s refrigerant circuits
We use 30 m. as a max length
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
21-05-2009, 01:59 AM #12
Re: length of each coil’s refrigerant circuits
desA,why you say so? It seems that you have that kind of experience, pls let me know? Thank you!
Using CFD to simulate two phase flow, especially including heat exchange, is extremely difficult, we need to use the right model, otherwise we would get the other way around.
Ok, Let's get to the point. Anyone has comment on the length of each coil's circuit? Pls do not hesitate to tell me, thank you!
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
MHI FDCA400HKXRE4 Tech Info Please
By L.JT in forum Trouble ShootingReplies: 5Last Post: 23-08-2008, 11:00 PM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM