Results 1 to 20 of 20
    May 2009
    Larson, Wisconsin
    63
    9
    Foamy compressor oil
    I recently changed complete oil charge on 2 RDB Plus Frick compressors and I have one that when running will foam completlely over top sight glass and appear the same in the bottom glass. Any insight would be greatly appreciated.
    Jul 2007
    Czech
    61
    374
    Re: Foamy compressor oil
    Liquid injection oil cooling, check thermal expansion valves+solenoid valve
    May 2009
    Larson, Wisconsin
    63
    9
    Sorry, themosyphon oil cooling.
    Jul 2007
    Czech
    61
    374
    Hi Winchester, you have the suction pipe 2 valves, 1 for manual valve should be closed, 2 strainer + on the return valve, it is sufficient to be open about 2x, offset pressures on 20-30 minutes
    Nov 2006
    veghel
    33
    Hey,
    oil temp ok?
    heating rods oke?
    Reagards.
    38
    Generally foaming oil indicates either saturated suction or oil is too cold, if too cold check the secondary oil recovery line after coalesars, if that is going hard out, oil is too cold. If the thermo system is controlled by one of those 3 way thermo valves wack it with a large hammer, as they can tend to stick after a prolonged shut down.
    thinking outload again.
    Magoo
    Jul 2007
    Czech
    61
    374
    Foam although other species (mineral-synthetic) or other oil producers
    Mar 2005
    638
    Did you change oil or add a different oil. No matter what the oil manufacturers say, mixing oils in a system can cause oil foaming...I've seen it happen.
    Ken
    May 2009
    Larson, Wisconsin
    63
    9
    Oil anylisis came back that oil viscosity was high and change complete charge with same oil.
    May 2009
    Larson, Wisconsin
    63
    9
    Oil temp at 138 running and all oil heating elemets working.
    May 2009
    Larson, Wisconsin
    63
    9
    Amot valve is working and holding a running oil temp. of 138. Oil return from coalescent filters is warm and no oil in sight glass.
    Apr 2009
    Durban
    70
    What is your saturated condensing temp and refrigerant? Condensing temp may be too low!
    Valrico, Florida
    509
    Are both compressors you changed the oil on running at the same pressures? Were all the filters changed (Oil and coalescent) on both compressors. As TXiceman stated mixing manufacturers oil can cause oil foaming.
    Sep 2008
    Canada
    811
    This is booster or high stage compressor.
    3,362
    Winchester ,
    Does your compressor have an economizer conected to comps and what conditions is it running at ?
    I think if you touch/feel/ observe frost patterns on and around compressor then you may spot some form of flood back .
    Rotor housing should get hotter as it approaches discharge end of machine .
    It would be nice to know temps and pressures ie discharge temp , suction / discharge pressures , oil level ( may be low ) ,economizer if any .
    Sometimes you can shut a plant down for a few hours and oil can settle in level control columns etc .
    Also check for unusual frost or lack of it on control columns on vessels . Float switches become sluggish and probes go haywire causing flood overs .
    May 2009
    Larson, Wisconsin
    63
    9
    This a booster compressor.
    Sep 2008
    Canada
    811
    Quote Originally Posted by Winchester View Post
    Usually, oil foaming happen when you overcharge oil or when liquid ammonia enter the oil separator. In your case may be thermosiphon heat exchanger has a leak. Check it.
    Jul 2007
    Czech
    61
    374
    You good choice oil filter?
    Apr 2002
    Nova Scotia, Canada
    55
    22
    On single stage screws, you will see the oil foam if the discharge pressure drops, such as when condenser pumps or fans start. Is the intemediate pressure stable or is there loads going on and off that may cause pressure flucuations.
    J.D
    Apr 2009
    Durban
    70
    Good Call J.D.
    Winchester, are you working on a booster high stage plant and are both compressors running at the same suction and discharge conditions or is one high stage and the other low stage?
    Frank Day
  1. White foamy oil?
    By marc5180 in forum Fundamentals
    Last Post: 24-03-2009, 05:47 PM