    Indoor fan motor??



    Arrived at a job today and found that the indoor fan motor was not running (no noise at all), when i tested for voltage on the 500V AC range between FAN HIGH and NEUTRAL i got a spark and the unit CB & RCD tripped.

    I also tested the 4uF capacitor and got a reading of 1.8uF.

    What is this info telling me? down to earth winding or shorted winding?

    I didn't have a insulation tester on me to perform any further tests?
    Last edited by airflo; 15-05-2009 at 09:11 AM.



  2. #2
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Actron indoor fan motor??

    the spark sounds to me like you touched ur probe onto an earth surface when you were testing the voltage.

    It will require a new cap.

    Was the motor hot at all?

  3. #3
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Actron indoor fan motor??

    Didn't actually feel the motor, and i only touched the probe on the NEUTRAL and FAN HIGH.

    Exactly what i thought its as though it was earthed? could the motor be down to earth? If so i should have got a belt from the case true?

    Could this be as simple as a faulty cap?

  4. #4
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Actron indoor fan motor??

    Faulty multimeter is what it was!!! its a cheapo chinese one anyway.

    But still not sure as to what the problem with the fan is? should i go back and try changing the capacitor?

    As i said the fan doesn't hum/make a noise or spin at all, but there is obviously power there or the above wouldn't have happened. true?

  5. #5
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Actron indoor fan motor??

    caps as far as i know should be +/- 10% so that ones way off the mark, a quick test if you think the start cap is dead is to simple turn the fan blade manually and if everything but the cap is o.k the fan motor will start, as you said the motor wasn't "humming" i would say there is a problem elsewhere also.

  6. #6
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Actron indoor fan motor??

    hey airflow what brand of motor are in actron air units? can you change the speed and see if the motor works. also i would start with a new cap as some good motors are thrown away all because of a faulty cap

  7. #7
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Actron indoor fan motor??

    Hello Airflow. You have already most probably found the fault. Anyway. Switch off the wires, take with your tester the resistive measure between every motor imput - on the scale of up to 1 KOhm
    (your motor should have it in a region of 50 - 300 Ohms). If OK between every a contact - and in case you do not have a megaohmeter - measure between any imput and the casing (ground) with a naximal scale (there are 10 MOhms on my one). Tester should measure nothing ("'continuity"', no digits at all) - if less than 1 MOhm - motor faulty.
    If all good, if fan turns good by hand, put a new capacitor and switch the motor not through the RCD but through a conventional, rated to the current of the motor
    (read from the plate), automatic switch and a current tong put on the live wire. Turn on power - current should not be higher than on the motor plate. If you have no tong, be near the motor (with aotomatic switch in the hands and one ear close to the motor), switch, if no turning and/or hum is heard, it needs repair.
    Sorry for the hasty, long bla-bla.

Similar Threads

  1. 1ph motor instead of 3 ph motor.
    By SPBDASAN in forum Electrical
    Replies: 1
    Last Post: 20-02-2009, 07:56 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. help with testing 3 phase comp
    By mat in forum Fundamentals
    Replies: 7
    Last Post: 19-01-2007, 09:03 AM
  4. locked rotor amps (LRA)
    By vinod in forum Technical Discussions
    Replies: 16
    Last Post: 09-09-2006, 12:50 AM
  5. Fan motor over heating & Shuting down.
    By Rookie in forum Domestic
    Replies: 15
    Last Post: 30-06-2005, 11:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •