Results 1 to 27 of 27
    Sep 2008
    india
    scroll compressor failure
    i facing a problem that the copeland scroll compressor dont building a pressure .
    The pressure are 160 PSIG at suction and discharge both end is same .
    Also compressor is taking 10 A current.
    Sep 2008
    india
    Re: scroll compressor failure
    can anyone suggest me what are checkpoint to diagnoss the problem.
    Jan 2008
    India
    70
    171
    If suction and discharge are high then it is overcharged.
    Please remove refrigerant and ensure the suction is around 65 /70 psig and discharge is 240 psi if the ambient is 35 for R-22.
    please measure the subcooling and superheat so that clear picture can emerge
    Aug 2008
    Baltics
    786
    Check phase sequence.
    Aug 2008
    Baltics
    786
    I mean your scroll may be turning in the wrong direction.
    Sep 2008
    india
    first we find that the compressor is taking 80A current
    Then we check the terminals at compressor end we found loaas terminal .
    Then we started the system we found the leakage .
    By brazing and vaccuming the system we charged the refrigerant from suction side we found the pressure is not builting . For that purpose we check the current the current is 10A i.e. normal.
    I think that there sholud bre failure of Scroll hence the motor is running bt not biluding the pressure.
    Can Anyone suggest on this?
    Aug 2008
    Baltics
    786
    Probably, first your system started loosing refrigerant, the reduced amount of gas did not cool the comp, the latter heated, thermically expanded and jammed. The loose contacts are, probably, the result of the monstrous current of the jammed motor. When the comp cooled down and the jam went it run, but, on my view your compressor now needs opening and repair.
    Aug 2008
    Baltics
    786
    The current and compressor's thermal protection need be improved, I wonder how motor's windings survived.
    Feb 2009
    PAKISTAN
    43
    dear
    there is only two posibilities
    one is the compressor which you are using is auto stop modle in this model the comp has a internal safty when comp will heat up due to high or low votage or any other reason the comp will stop its pumping and you have to switch it off for three or four hours
    Second is this you have to check you phase sequence it should be clock wise
    Note
    if the suction pressure will too low then the comp will react same like that
    Split Croatia
    6,151
    Is that unit heat pump with 4-way valve?
    Sep 2008
    india
    Our scroll compressor is opening on ASTP .
    What are the resaons can anyone suggest .
    Split Croatia
    6,151
    ASTP is Apollo-Soyuz Test Project?
    Sep 2008
    india
    As we know the ASTP opens at Critical Temp i.e. 135 Deg C.
    The reasons will be loss of refrigerant , gas quantity low. But in this case gas quantity is ok . also there is no refrigerant leak.
    Also condenser and air flow is OK .
    The compressor is ZR94 having Capacity 23.3 KW
    and POwer consumption is 6.75 KW .
    Is condenser is Short?
    Thats Why The discharge temperature is overshooting.
    Sep 2008
    india
    Please give your comments
    Split Croatia
    6,151
    Quote Originally Posted by sagar45 View Post
    We can not comment further if you don't answer at asked questions!
    May 2006
    India
    399
    Compressor is not probably pumping ; current drawn mentioned could be the magnetising current.
    Mar 2007
    INDIA
    42
    To confirm the compressor pumping effect through the following ways:
    Method 1: By expansion valve
    Step 1; Take out the expansion valve bulb from evaporator outlet and immersed into a cold water (probably 20 Deg C less than ambient)
    Step 2: Check the suction pressure reduction is happening drastically / not
    Step 3: If suction pressure reducing drastically than compressor pumping is ok. If not compressor pumping is failed.
    I hope this will help you to resolve the issue.
    Regards,
    Ravi perumal
    senthil_idmc06's Avatar
    senthil_idmc06 Guest
    Dear All,
    It's a well equipped PLC based vapour compression system. We are using grasso screw compressor. One of the compressor is getting trip often, That time it's control panel gets the "alarm 37 " .I went through the manual and observed that there is some loose connection or defective module.
    I rectified the above factors. Then also it's getting trip some times.
    can any one suggest some other possible causes.
    Senthil
    Jun 2009
    hilton head island,s.c.
    63
    7
    If both suction and discharge are the same then the valves are bad, the amp draw should be 75% of the RLA on the M# tag
    Sounds like the scroll is screwed.
    Hey Nike. I did enyoy, LMAO, your reference "Apollo Soyus Test Project" what ever connection.
    The first time I have seen a Croatian sense of humour.
    magoo
    May 2008
    66
    802
    Hey Magoo,
    you aint seen nothing yet dan. don't leave the gate open for Nike he become's unstoppeble. (LOL)
    Ice
    Split Croatia
    6,151
    Quote Originally Posted by senthil_idmc06 View Post
    D
    Senthil
    I suggest that you start your own thread, and not stealing someone other thread.
  23. #23
    Nov 2007
    London
    461
    either reverse phase if it is noisy, or the scroll is damaged.
    if it is a new comprressor you will have your phases reversed or the 4 way valve is jammed in between and you are pumping your discharge into your suction.
  24. #24
    Split Croatia
    6,151
    Quote Originally Posted by icecube51 View Post
    Hey Magoo,
    Ice
    Ice???
  25. #25
    Split Croatia
    6,151
    Quote Originally Posted by brunstar View Post
  26. #26
    Split Croatia
    6,151
    magoo
    It is not that original.
    Someone say ASTP and you go like this:
    http://tinyurl.com/p7m6yv
    And third result is:
    http://en.wikipedia.org/wiki/Apollo-Soyuz_Test_Project
    Others doesn't make any sense with this thematic.
  27. #27
    Jun 2009
    limassol
    61
    7
    For sure your problem is wrong turn.change immediately one phase if is 3phase motor or change running by starting in 1phase
  1. Copeland Scroll Advanced Protection Problems
    By dwayne in forum Trouble Shooting
    Last Post: 24-09-2010, 06:54 AM
  2. Digital scroll
    By archibaldtuttle in forum Commercial
    Last Post: 06-01-2010, 05:27 PM
  3. Scroll internal bypass
    By Larry2 in forum Heat Pumps
    Last Post: 15-05-2009, 09:23 AM
  4. copeland ZR scroll vs VR scroll
    By Lc_shi in forum Technical Speculations
    Last Post: 03-09-2008, 04:27 PM
  5. Hermetic reciprocating versus hermetic scroll
    By Cofreth in forum Technical Discussions
    Last Post: 19-11-2005, 06:29 PM