    Controlling on/off valve



    Hi everyone,

    I'd like to ask assistance in solving a technical/control issue for a system I'm working with. I'm a mechanical design engineer, new to the hvac industry & very inexperienced on the practical control side. So, please bear with me.

    Concept:
    Open the valve, when the compressor operates
    Close the valve, when the compressor is off.

    I've included two sketches below of my thoughts.





    Technical questions:
    I'm looking for a budget, simple way on how to do this.
    What type of valve?
    How to convert the compressor ON/OFF to a valve OPEN/CLOSE operation (controller, switch?)
    Can the compressor activation signal (controller, or otherwise) be used to activate the valve? If so, how?

    Help from the forum guru's would be ever so gratefully accepted. Thanks folks.
    Last edited by desA; 14-05-2009 at 04:34 AM.



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Controlling on/off valve

    In accordance with the information you have provided, switch the drive of the valve through an additional NO (normally open) contact on the compressor's contactor. Unless you describe the system the compressor and the valve are parts of, I suspect, nobody will give you a better advice.

  3. #3
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: Controlling on/off valve

    yuri b is spot on .... end of thread

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling on/off valve

    Quote Originally Posted by Yuri B. View Post
    In accordance with the information you have provided, switch the drive of the valve through an additional NO (normally open) contact on the compressor's contactor.
    Thanks, Yuri.

    So, can I take it that you're saying that you can drive a solenoid valve via an NO (normally-open) contactor from the compressor?

    This would make good sense - nice & simple.

    I'd been trying to work through having to use a lower-power control circuit etc, but a direct power contact from the compressor would seem to be very elegant.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Controlling on/off valve

    On simple refrigeration systems, working without pump down on stop, contactor, starting the compressor, energizes the liquid solenoid valve - on stopping, closes it. Let the valve in your system, no matter what intended for, be just controlled similarly.

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling on/off valve

    Thanks, Yuri...

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Controlling on/off valve

    Using an additional contact on the compressor contactor will open the valve whenever the contactor is energised, even if the compressor is not running, for what ever reason.

    A better way to do it to ensure that the compressor is actually running before opening the valve is to use a current sensing device on the compressor wiring

    http://www.electrocontrols.co.uk/datasheets/Q01.pdf

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling on/off valve

    Thanks very much, Frank.

    That is a very elegant solution, which will be sure to also be useful in a whole host of applications. Excellent.

  9. #9
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Controlling on/off valve

    Well. That a compressor draws current - even its nominal one - still does not mean that it is working properly (leaky compression valves, phase changed on a screw comp, etc). Besides, current control is rather expensive: current transfoormer + microprocessor + relay output. More reliable and cheaper would be a simple mechanical thermostat on the discharge pipe, near the condenser input (set, let's say at 60 C). A closed circuit - NO contact on the comp contactor in sequence with the contact on the thermostat - would be a secure cofirmation that the compressor works (and makes compression).

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Controlling on/off valve

    Looking at schematics reminds me of a "Carrier" liquid feed control to heat exchanger TEV. Simple liquid control and reduced cost of liquid solenoid valve. When compressor stops the pilot three way solenoid interruped the external equalizer line and injected HP liquid pressure on top of TEV and slammed TEV shut, simple shut off valve.
    Old is not necessarily wrong.
    magoo

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling on/off valve

    Quote Originally Posted by Yuri B. View Post
    Well. That a compressor draws current - even its nominal one - still does not mean that it is working properly (leaky compression valves, phase changed on a screw comp, etc). Besides, current control is rather expensive: current transfoormer + microprocessor + relay output. More reliable and cheaper would be a simple mechanical thermostat on the discharge pipe, near the condenser input (set, let's say at 60 C). A closed circuit - NO contact on the comp contactor in sequence with the contact on the thermostat - would be a secure cofirmation that the compressor works (and makes compression).
    Thanks again, Yuri.

    The aim is to keep the solution as simple & inexpensive as possible. The series solution of NO compressor contact & thermostat is good, as it also brings in additional temperature control functionality - at a reasonable on-cost.

    Excellent.

  12. #12
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling on/off valve

    ^^ Thanks for your wisdom, Magoo.

    So many ways to solve this case.

  13. #13
    Join Date
    Jan 2009
    Location
    australia
    Age
    68
    Posts
    16
    Rep Power
    0

    Re: Controlling on/off valve

    You're a bit wooly with the description but it seems you need a solenoid operated valve energised from the compressor control circuit

  14. #14
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling on/off valve

    Thanks 'bowral_fridgy'.

    There have been some excellent suggestions & I'm now fairly comfortable in a useful solution.

    I purposefully left the description a little 'fuzzy' as it could apply to a number of devices.

Similar Threads

  1. Replies: 2
    Last Post: 06-02-2009, 07:35 PM
  2. Oversize Relief Valve
    By Dacosta in forum NH3
    Replies: 1
    Last Post: 05-09-2008, 11:35 AM
  3. Compressor valve test
    By RackMechanic in forum Air Conditioning
    Replies: 11
    Last Post: 03-02-2008, 05:57 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •