13-05-2009, 05:25 PM #1
do u need an accumulator on a chiller?
do u need an accumulator on a chiller? Is there a way to omit the accumulator on a chiller?
-
13-05-2009, 05:45 PM #2
Re: do u need an accumulator on a chiller?
Accumulators are needed where reduction in heat load can result in floodback to the compressor. On most systems they are not needed... so the answers to your questions are: maybe and maybe.
-
13-05-2009, 09:31 PM #3
Re: do u need an accumulator on a chiller?
On a water chiller, it is seldom used. I can say that none of the primary chiller manufacturers I know of install accumulators on the suction.
-
14-05-2009, 12:52 PM #4
Re: do u need an accumulator on a chiller?
Load variation is main issue. Most chiller manufacturers do it out of abudent pre-caution against floodback since load variation is out of their control when chiller is delivered to customer.
-
14-05-2009, 01:59 PM #5
Re: do u need an accumulator on a chiller?
water chiller? blast chiller??
constant load no
vari load yes..... but it will not do any harm to fit one ..any thing that stops liquid is a good thing
-
14-05-2009, 02:07 PM #6
Re: do u need an accumulator on a chiller?
It is used for safety purpose. If there is a variable load on evaporator accumulator is used. For small capacity water chiller accumulator is rarely used. To omit accumulator, u use thermostatic expansion valve, to feed the evaporator according to load.
-
14-05-2009, 04:28 PM #7
Re: do u need an accumulator on a chiller?
If you are talking of Water / brine chiller accumulators are not needed.
If it is cold room refrigeration system accumulators may be required.
-
14-05-2009, 05:31 PM #8
Re: do u need an accumulator on a chiller?
It all depend on design and working conditions.
Some manufacturers have them and some don't.
-
16-07-2010, 09:57 AM #9
Re: do u need an accumulator on a chiller?
yes i need this thanks for this post
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Dunham Bush Chiller Alarm
By Regulator in forum Air ConditioningReplies: 11Last Post: 08-12-2010, 01:42 AM -
Absorption Chiller VS Mech. Chiller
By Intern in forum IndustrialReplies: 20Last Post: 30-05-2009, 08:31 AM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM