12-05-2009, 05:04 PM #1
Sullair C25SB
This is a booster compressor that runs at 12" and the problems is that on start up it fails on low oil pressure. It does biuld oil pressure. What I have noticed is that the oil and discharge pressures equalize to suction pressure went it's off so when it starts it times out on low oil pressure. I have changed oil pump check and oil injection to male and female rotor. Any insight would be greatly appreciated. Thanks
-
12-05-2009, 08:45 PM #2
Re: Sullair C25SB
When idle it is not abnormal for the complete package to be at suction pressure.
My first question is the oil strainer clean that supplies the oil pump? It is probably a 1-1/2" Y strainer unless it has the optional dual basket style. Your oil level should be in the middle of the top sight glass, you should have 3, at the bottom of the oil separator.
You can contact me at dan@midstatesrefrig.com
-
13-05-2009, 09:39 AM #3
Re: Sullair C25SB
If the package is in a vacuum on start up it may be difficult difficult for pump to prime properly , maybe this is the case ?
On some sullairs the pump stops once timed out to give chance for pressure differential to take over oil feed .
Oil pump pre filter as suggested and main oil filter could be checked as well .
Is oil seperator oil heater working when compressor idle ?
-
19-05-2009, 04:12 PM #4
Re: Sullair C25SB
We had a similar problem with our Sullair and it was the strainer, it was clogged. Once we cleaned it it ran fine.
Similar Threads
-
Sullair Booster Compressors
By Bunnyengr in forum Technical SpeculationsReplies: 10Last Post: 10-06-2009, 06:53 PM -
Sullair manuals?
By CJDEZ in forum Industrial CompressorsReplies: 4Last Post: 08-04-2009, 01:38 AM -
Sullair C Series and CB Series
By Oz Fridgey in forum Industrial CompressorsReplies: 3Last Post: 18-02-2009, 09:44 PM -
Sullair Ammonia Compressor
By nh3wizard in forum Industrial CompressorsReplies: 16Last Post: 29-01-2009, 10:14 PM