    Basic question about recovering



    Hello all,
    Im still new to this scene and am Still learning about everything, and would be gratefull of any advise given. Just a few quick questions of things I am a little unsure of:
    First of all, When Recovering do I recover just into the vapour valve on the recovery cylinder or liquid? Or do I swap over accordingly?
    Also what is the correct way to determine the condenser operating temp? (The unit I am currently working on is a lennox package with R407c.)To work out my pressure test value when leak detecting.
    Hope this makes sense, Thanks in advance for any help given



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Basic question about recovering

    If you are recovering with a single hose, not doing a push/pull, then it doesn't matter which valve you use. It all ends up in the same place.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Basic question about recovering

    Ar Thanks Brian,
    Thats what I thought it was just for piece of mind check Im doing the process correctly.

  4. #4
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Basic question about recovering

    Hi lees8110,

    Also what is the correct way to determine the condenser operating temp? (The unit I am currently working on is a lennox package with R407c.)To work out my pressure test value when leak detecting.
    To work out the minimum leak test pressure, you would use the values from the table in BS EN 378:2008, which are for UK,

    High side with air cooled condenser 55C
    High side with evaporative condenser 43C
    Low side 32C

    So you need to work out the saturation pressure of the refrigerant for those temperatures. Note use the liquid scale on your comparator.
    Tony

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Basic question about recovering

    For Fujitsu R407 VRF leak test pressure is 2,94MPa for 24 hours. Change of pressure with temperature is 0,01Mpa/1K

  6. #6
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Basic question about recovering

    Spot on tony thanks for that
    I remember doing it now,

    thanks again

Similar Threads

  1. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  2. basic fridge question
    By weidit in forum Fundamentals
    Replies: 13
    Last Post: 08-05-2009, 07:52 AM
  3. r134a question, calculating heat lost by refrigerant
    By kamikazi929 in forum Fundamentals
    Replies: 0
    Last Post: 03-01-2008, 08:19 PM
  4. Basic question about refrigerant to use
    By cbfull in forum Fundamentals
    Replies: 25
    Last Post: 07-08-2007, 02:19 AM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •