    L’Unite Hermetique



    I have the following compressor-
    Make - L’Unite Hermetique

    Model FH4524F

    Gas R22

    Manufacture date 13/11/2000
    Can anyone advise what size coolroom it will sevice. The temp I need to get to is 2-3 degrees celsius



  2. #2
    Join Date
    Mar 2008
    Location
    Melbourne, Australia
    Age
    40
    Posts
    48
    Rep Power
    0

    Re: L’Unite Hermetique

    It is fine to say that you have a compressor but that is only one component of what you need to have a refrigeration system.

    It would be good to have some more information about what you are trying to do?

    One would assume that your trying to make a coolroom. If that is the case, it would be better to design the coolroom to the size that you need, rather than base the size of the room on a 2nd hand compressor that has probably seen better days!

  3. #3
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: L’Unite Hermetique

    Here is a site where you can find your unit do search for fh4524f condensing unit its there

    http://www.tecumseh-europe.fr/index.php

    Norm
    Last edited by Toosh; 11-05-2009 at 10:13 PM.
    My wife used to say you never listen to a word I say at least I think that what she said

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: L’Unite Hermetique

    That unit has 3300W at Te -5°C and Tc 50°C (ambient 35°C), suction temperature 20°C, subcooling 3K. It could serve room from 5m^3 to 150m^3.
    Last edited by nike123; 14-05-2009 at 07:24 AM.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: L’Unite Hermetique

    Quote Originally Posted by nike123 View Post
    That unit has 3300W at Te -5°C and Tc 50°C (ambient 35°C), suction temperature 20°C, subcooling 3K. It could serve room from 5m^3 to 150m^3.
    But only if that compressor works.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: L’Unite Hermetique

    halo,im new here... can somebody show me the calculation pls.....
    thanks a lot.....hongfain@hotmail.com

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: L’Unite Hermetique

    Quote Originally Posted by ah fai View Post
    halo,im new here... can somebody show me the calculation pls.....
    thanks a lot.....hongfain@hotmail.com
    http://www.ishrae.in/journals_20042005/2005july/article06.html
    Last edited by nike123; 16-05-2009 at 03:05 PM.

Similar Threads

  1. L'unité hermétique FH-4525-YHR 220V/1/50Hz
    By Joeri in forum Electrical
    Replies: 6
    Last Post: 07-06-2008, 11:47 PM
  2. l'unite hermetique R12 Condensing unit
    By airefresco in forum Commercial
    Replies: 13
    Last Post: 08-02-2008, 09:08 PM
  3. L'Unite hermetique wiring
    By Chilly willy in forum Electrical
    Replies: 11
    Last Post: 20-08-2007, 06:38 AM
  4. L'Unite Hermetique compressor
    By iceman007 in forum Commercial
    Replies: 4
    Last Post: 27-06-2004, 08:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •