    Danfoss fan speed controller



    I have some DX systems with danfoss fan speed conrollers RGE X3R4-7. These systems were fitted, filled and supposedly commissioned. I was initially having a problem with compressor tripping on HP as the air cooled condensers weren't comming in. I have reduced the pressure setpoint on the controller as this was still at factory setting and the fans now come in. Could anybody give me some advice on how i determine the correct pressure to set on these controllers.
    Thanx



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Danfoss fan speed controller

    By turning the "adjusting screw" on the device (says the brief instruction I found in a matter of few seconds, thanks to our old friend Google). Your device is intended for work with R22 , R404, R407C. So, according to the refrigerant type used in your systems.

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Danfoss fan speed controller

    I am an electrician working in HVAC and may turn to be dissaproved by profi refs, but I usually set 33-35 C to maintain no matter what refrigeration, with 1,5 -2 Bars differential.

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Danfoss fan speed controller

    Differential, however, should be a fixed one in your device.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Danfoss fan speed controller

    Much fuss, little fun. By 33-35C is meant condensing temp (read on the "clock").

  6. #6
    Join Date
    Jun 2008
    Location
    Russia
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Danfoss fan speed controller

    Thanx guys

    The manufacturers data said a condensing temperature of 38 deg c so i set to around 36 deg c, 13.5 bar for 407C. Just wanted to be sure.

Similar Threads

  1. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 02-02-2009, 12:23 AM
  2. Upgrading Danfoss AK2 controller
    By interop in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 16-10-2008, 02:06 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 08:23 PM
  4. Fan speed controller set up
    By Ianh in forum Technical Discussions
    Replies: 7
    Last Post: 09-01-2006, 08:48 PM
  5. Fan Speed Controller
    By Abe in forum Commercial
    Replies: 3
    Last Post: 02-06-2004, 05:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •