    converting a calculation to Si

    I have just read a post from a few years back and have noticed this
    "Most condensors operate at a close to estimated temperature of 30 degrees F over ambient.
    So if we know what the ambient is and add 30 degrees F to it we can safely estimate,

    Lets take a look at the suction pressure
    similiar as above excecpt normal operating sytems have an average coil temp of 15 degrees f
    below temp controlled area".

    But if i were to convert these temps to DegC then 30F would be -1.1DegC
    and 15f would be -9.44, surely this cant be right for si units?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: converting a calculation to Si

    You have two things when converting Fahrenheit to Si units.
    First is actual temperature which is converted in Celsius degree and second is temperature interval converted in Kelvin

    You need to distinguish in text what is what and corectly convert that.

    Fahrenheit temperature is converted in Celsius degree by subtracting 32 from Fahrenheit temperature and than multiplied by 5/9.
    Fahrenheit temperature interval is converted in Kelvin by multiplying Fahrenheit interval with only 5/9.

    In your example:
    30°F=30x5/9=16,6666666K
    15°F=15x5/9=8,33333333K

    For ambient temperature:

    40°F=(40-32)x5/9=8x5/9=4,44444444°C
    Last edited by nike123; 10-05-2009 at 09:51 PM.

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: converting a calculation to Si

    ok so in si units, head pressure should be roughly ambient + what in DegC

    and also suction pressure should be space temp - what in DegC?

    Just as a rule of thumb.

    Ah ok just noticed your edit so the head pressure should be 16Deg C and the sp 8DegC?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: converting a calculation to Si

    Quote Originally Posted by marc5180 View Post
    ok so in si units, head pressure should be roughly ambient + what in DegC

    and also suction pressure should be space temp - what in DegC?

    Just as a rule of thumb.

    Ah ok just noticed your edit so the head pressure should be 16Deg C and the sp 8DegC?

    Read again more carefully. It is once more edited.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: converting a calculation to Si

    If you have condenser air in temperature of 30°C than 30°F over ambient would be 46,66666°C
    If you have air in temperature at evaporator of -18°C than 15°F below ambient would be -26,3°C.

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: converting a calculation to Si

    Now you've got me, where have you got 46.6 and 26.3 from? Im confues because you are using both °C and °F.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: converting a calculation to Si

    Quote Originally Posted by marc5180 View Post
    Now you've got me, where have you got 46.6 and 26.3 from? Im confues because you are using both °C and °F.
    Quote Originally Posted by nike123 View Post
    You have two things when converting Fahrenheit to Si units.
    First is actual temperature which is converted in Celsius degree and second is temperature interval converted in Kelvin

    You need to distinguish in text what is what and corectly convert that.

    Fahrenheit temperature is converted in Celsius degree by subtracting 32 from Fahrenheit temperature and than multiplied by 5/9.
    Fahrenheit temperature interval is converted in Kelvin by multiplying Fahrenheit interval with only 5/9.

    In your example:
    30°F=30x5/9=16,6666666K
    15°F=15x5/9=8,33333333K


    For ambient temperature:

    40°F=(40-32)x5/9=8x5/9=4,44444444°C
    ..........................
    Last edited by nike123; 10-05-2009 at 09:51 PM.

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: converting a calculation to Si

    Ok so for example if i had a condensor air in of 30°C then (40°F for example only) over ambient would be 52.22°C.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: converting a calculation to Si

    I hoped there would be a simple way to check like the way the quote sounded

    Discharge pressure should = say 15°C plus the ambient
    Suction pressure should = say 10°C plus ambient (RA).
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: converting a calculation to Si

    Quote Originally Posted by marc5180 View Post
    I hoped there would be a simple way to check like the way the quote sounded

    Discharge pressure should = say 15°C plus the ambient
    Suction pressure should = say 10°C plus ambient (RA).
    http://www.refrigeration-engineer.co...75&postcount=5

    All values here should be in Kelvins, but amount is same.
    Last edited by nike123; 10-05-2009 at 08:38 PM.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: converting a calculation to Si

    Quote Originally Posted by marc5180 View Post
    Ok so for example if i had a condensor air in of 30°C then (40°F for example only) over ambient would be 52.22°C.
    Yes, you got it.

Similar Threads

  1. how can we calculation industrial refrigeration
    By lam sanh in forum System Optimization
    Replies: 34
    Last Post: 28-02-2011, 01:31 PM
  2. Flash gas calculation software
    By nike123 in forum Tools and Calculators
    Replies: 4
    Last Post: 12-03-2009, 09:25 AM
  3. Calculation bypass buffer tank volume
    By abbasi in forum New Technologies
    Replies: 3
    Last Post: 16-10-2008, 06:19 AM
  4. Replies: 3
    Last Post: 27-11-2007, 10:00 AM
  5. Cooling load calculation
    By raviperumal in forum Technical Discussions
    Replies: 6
    Last Post: 02-03-2007, 04:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •