Results 1 to 16 of 16
  1. #1
    Join Date
    May 2009
    Location
    United States
    Age
    70
    Posts
    5
    Rep Power
    0

    experimental evaporator



    hi i'm using a BD35F condensing unit, my evaporator is experimental, meaning i made it out of 1/4" tubing and it chills a copper plate that chills water running over it. my evap frost up well but it fluctuates, it frost then the frost disappears then frost again, also the cap tube .031 id 9' long frostup about an inch or two before it enters the evap, anyone have an idea of what i can do to improve the performance?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    Before you can determine if a system is doing what it's supposed to do, you need to know what it's supposed to do.

  3. #3
    Join Date
    May 2009
    Location
    United States
    Age
    70
    Posts
    5
    Rep Power
    0

    Re: experimental evaporator

    Gary,
    thank you for the response and you are right I did not provide enough information and my knowledge is also limited. this is what I'm trying to do. I'm sitting this BD35F condensing unit with a fan cooled condenser on top of a reservoir of water which sits on top of a copper plate which sits on top of a coil consisting of 4 passes of 1/4" tubing about 10" long. the water is circulated over the plate and through plastic tubing. i only want the water to chill to about 60 degrees F. leaving the reservoir. my cap tube is over 9' long which I did so that if I have to remove some, well it is easier than adding. now i did not have it under load conditions but my evaporator did frost up through all passes right up to the end of the evaporator. but it would fluctuate frosting then unfrosting. today I'm putting it under load conditions and testing again, i expect to have to remove some cap tube.any help you could give me would be appreciated Gary, Thank you.- PS if you need any specific info please ask. I'm not a engineer just a service man trying to please his boss-respects, Chuck

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    When the reservoir is down to 60F, then we need to know the reservoir water in and water out temps, the condenser air in and air out temps, the high and low side pressures, the liquid line temp near the receiver outlet (or condenser outlet if there is no receiver) and the suction line temp near the evaporator outlet.

    Also we need to know what refrigerant you are using.
    Last edited by Gary; 11-05-2009 at 05:40 PM.

  5. #5
    Join Date
    May 2009
    Location
    United States
    Age
    70
    Posts
    5
    Rep Power
    0

    Re: experimental evaporator

    Hi Gary! yesterday i cut the cap tube down to 7' my low side pressure was about 5-psig, my high was about 100-psig, my ambient was about 86-f, and we were getting about about 58-f out of the reservoir. they will be testing it this weekend and when they get back I'll get all of the information you asked for early next week. I don't believe this is correct yet as i was getting better results with the 9'+ cap. we are using R134a. Thank you Gary for your time and input, Respects, Chuck

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    At 100psi your saturated condensing temp (SCT) is about 87F. Since the ambient is 86F, the SCT is only 1F over ambient. This means the refrigerant is picking up almost zero heat load in the evaporator. A full heat load would put the SCT about 20-35F above ambient.

    Similarly, at 5psi the saturated suction temp (SST) is about -4F. This is about 62F below the temp of the water, confirming the lack of heat flowing from water to refrigerant.

    There could be a variety of causes and/or multiple causes for this, but we can't tell what is wrong without all of the numbers.

    All we can tell at this point is that something is very wrong with this picture.
    Last edited by Gary; 12-05-2009 at 08:35 PM.

  7. #7
    Join Date
    May 2009
    Location
    United States
    Age
    70
    Posts
    5
    Rep Power
    0

    Re: experimental evaporator

    Thanks Gary, again, before I cut 2ft.of cap tube off I was reading 150 psig and 0 psig on the low. at any rate look for me monday afternoon or tuesday morning I'll have the info, respects, Chuck

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    Those numbers are even worse. Less heat transfer in the evaporator and higher head = liquid backing up in the condenser/overcharge.

    How are you charging the system?
    Last edited by Gary; 13-05-2009 at 01:10 AM.

  9. #9
    Join Date
    Jan 2009
    Location
    sunny norfolk
    Posts
    81
    Rep Power
    16

    Re: experimental evaporator

    any chance you could put a TEV on it and see what that gives you. Capillary is a bit of a nightmare to set up and fitting a TEV will rule out the incorrectly sized expansion device

    regards
    steve

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    Quote Originally Posted by 123-steve909 View Post
    any chance you could put a TEV on it and see what that gives you. Capillary is a bit of a nightmare to set up and fitting a TEV will rule out the incorrectly sized expansion device

    regards
    steve
    That's a good point, Steve. In order to evaluate and optimize the performance of the experimental evaporator, we first need to optimize the cap tube... and that is going to take a lot of work.

    It involves balancing the subcooling against the superheat, step by step, with presumably much cutting and recharging... a nightmare indeed.

    Installing a TXV could make the task much easier as the TXV will automatically optimize itself.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    If it is necessary to balance the cap tube, here is how it's done:

    Charge the system until the liquid line subcooling is 15F/8.5K.

    Wait until the water in the reservoir is down to the desired temp.

    Check the superheat near the compressor inlet.

    If the compressor inlet superheat is less than 20F/11K, then very slowly remove refrigerant until the superheat is 20F/11K.

    If the compressor inlet superheat is more than 20F/11K, then the cap tube is too restrictive and needs to be shortened.

    Repeat these steps until the correct compressor inlet superheat can be achieved without exceeding the 15F/8.5K subcooling limit.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: experimental evaporator

    I should point out that the above strategy balances the cap tube output against the current heat load. Once this is done we can evaluate the current performance of the experimental evaporator.

    If we then take steps to improve its performance (increasing surface area and/or increasing water flow), this will increase the heat load. Then we need to balance the cap tube all over again.

  13. #13
    Join Date
    Jan 2009
    Location
    australia
    Age
    68
    Posts
    16
    Rep Power
    0

    Re: experimental evaporator

    [quote=chuckstrain;144415] my evap frost up well but it fluctuates, it frost then the frost disappears then frost again,

    Sounds like moisture in system causing restriction in capillary hence low suction pressure

  14. #14
    Join Date
    Aug 2007
    Location
    Germany
    Posts
    36
    Rep Power
    0

    Re: experimental evaporator

    RTFM always thoroughly!
    Vacuum sucks!
    Sience rules!

  15. #15
    Join Date
    Feb 2001
    Location
    phoenix,arizona
    Age
    72
    Posts
    104
    Rep Power
    24

    Re: experimental evaporator

    being this is experimental; rather that keep cutting the cap tube, wouldn't it be easier using a adjustable valve (many ***** hose come with a shut off valve), keep adjusting this valve until you get the proper superheat.
    Be Happy

  16. #16
    Join Date
    May 2009
    Location
    United States
    Age
    70
    Posts
    5
    Rep Power
    0

    Re: experimental evaporator

    this is a 1/20 hp condensing unit. is there a a expansion valve that meters for that small of a unit?

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Designing Roll Bond Evaporator
    By Munzar Ata in forum Fundamentals
    Replies: 11
    Last Post: 05-08-2010, 11:31 AM
  3. Absortpion Refrigeration - Evaporator Basics
    By knudo in forum Fundamentals
    Replies: 4
    Last Post: 28-08-2007, 08:03 AM
  4. What is the best location for a evaporator fan?
    By Jasno999 in forum Fundamentals
    Replies: 3
    Last Post: 21-02-2007, 01:34 AM
  5. Change evaporator
    By tralex in forum Fundamentals
    Replies: 6
    Last Post: 29-12-2005, 08:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •