    we are working on a als series chiller one of the compressors keeps tripping on no liquid run fault i have been able to get a little info on a gate failure problem but where is the gate that keep fails or does any one know where i could get some info on the compressors to troubleshoot the gate if to see if this might be where the problem is
  2. #2
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17
    Re: Mcquay ALS screw faults
    The gate they are talking about is the star gate and that is inside the compressor and im afraid its a new compressor.