    Norpe dairy cabinet



    Went today to one of these units. Temperature inside the case is 15 degrees C. All the condensing unit and twin compressors underneath. Checked the cabinet, and as I was expecting it's warmer on one side and cooler on the other.
    Someone previously had installed 2 line tap valves, one in each suction line-saved me the bother.
    One compressor head temp is 55 degrees, the other 105 degrees, so straight away I thought there would be no gas. Took the pressures and the circuit with the higher temperatures on the compressor and discharge line has a suction pressure of 80 psi-it's on R404A by the way-gives an evaporating temp of 2 degrees-I would have expected -10 for this type of application. The other circuit suction is 40 psi-evaporating at -14 about right. During the defrost cycle, the case temp actually started to fall-evap fans are supposed to run on these units during defrost. In the condenser the inlet pipe temp is 65 and 55 degrees and outlet before the capillary is 27 and 26 degrees!!. But the delta T for the condenser airflow is only 4 degrees- on at 23 and off at 27. Anyway, I connected the gauges to the circuit which I had identified was a problem, and the standing pressure during the defrost is 95psi-which I had expected to be a bit higher in a 23 degree atmosphere. When the compressors start back up, theres hardly any pulldown and the suction pressure after 20 minutes is still 90psi-only dropping by a few psi, and way too high, both suction lines are at around 20 degrees, giving a massive superheat. Listened to the compressor and picked up an odd noise, like hissing gas. I thought that the suction valves were to blame, but there are no service valves so I can't try and pull a vac with the compressor, but think that the heat is being generated because this compressor is running but not pumping properly, so no condensing etc.
    Anyone have any other ideas??

    Regards
    James

    PS Apologies for the length of this thread.


    a problem shared is a problem halved

  2. #2
    Join Date
    Sep 2003
    Location
    South Yorkshire UK
    Age
    57
    Posts
    25
    Rep Power
    0

    Re: Norpe dairy cabinet

    Quote Originally Posted by iceman007
    this compressor is running but not pumping properly, so no condensing etc.
    Anyone have any other ideas??
    Sounds about right to me.......try stopping your evap fans and see if the suction pressure drops.

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Norpe dairy cabinet

    That was quick Mrchatts

    It was the most obvious one to me-also explains why one side is warm and the other colder- 2 evaporator coils I think. Looks like another compressor change!!

    Best Wishes
    James
    a problem shared is a problem halved

  4. #4
    Join Date
    Sep 2003
    Location
    South Yorkshire UK
    Age
    57
    Posts
    25
    Rep Power
    0

    Re: Norpe dairy cabinet

    Quote Originally Posted by iceman007
    It was the most obvious one to me-also explains why one side is warm and the other colder- 2 evaporator coils I think
    I’m not sure if there are two coils side by side, I would say the coils runs full length of the case and is shared by both units, one thing to check is that no Air con is blowing into the warm side Oh! and of course a super clean condenser is a must, not that you haven’t checked that already.

  5. #5
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Norpe dairy cabinet

    mrchatts you are probably right about the evaporator, the condenser has a similar set up, it's shared by both fridge circuits, one has the top half and the other has the bottom half, it's totally clean-funny enough the first job I had today was a dirty condenser-R22 85psi suction etc etc. Oh- and theres no a/c blowing on there.

    Many Thanks
    James
    a problem shared is a problem halved

  6. #6
    Join Date
    Sep 2003
    Location
    South Yorkshire UK
    Age
    57
    Posts
    25
    Rep Power
    0

    Re: Norpe dairy cabinet

    Have fun changing the compressor James, bet you can’t count how many you've changed this month

  7. #7
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Norpe dairy cabinet

    This will be my third in two weeks, plus I have another two air con ones to do-still I'm not complaining keeps me in a job.
    Funnily enough I've had loads of problems with these dairy cabinets, as I took a contract on for a supermarket, and the prevoius maintenance is hardly existent. They're paying now for the previous cutbacks-Being Pennywise and Pound Foolish I think is the expression

    James
    a problem shared is a problem halved

  8. #8
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Norpe dairy cabinet

    Hi Iceman,
    Comps are not too difficult to change on these have done plenty. Check he conderser fans, should be 10w but 7w ones are commonly incorrectly fitted because these were always easier to get hold of. Be very carefull as you pull the unit out as the driers and the cap tube are normally located behind the LH front leg and can easilly be kinked.
    Quick piece of advice if anyone ever gets called to one of these and only one comp works. The staging for the second compressor goes through a light tube fsu started in the electrics box to stop it coming on at the same time as the first (Quality !!!!!!! ).

    These units do suffer badly from blocked condensers & condenser fan problems.

    Regards

    Raymond

  9. #9
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Norpe dairy cabinet

    Hi Raymond

    I noticed the cap tubes and driers all squeezed in behind the left leg-both compressors running, just that one of them isn't doing the job properly. Not a difficult job to change it anyway. Should do the trick.

    James
    a problem shared is a problem halved

Similar Threads

  1. Duty For costan Dairy cabinet
    By Chris2005 in forum Commercial
    Replies: 1
    Last Post: 12-09-2005, 10:55 PM
  2. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  3. Dairy Cabinet
    By iceman007 in forum Commercial
    Replies: 6
    Last Post: 03-07-2004, 11:39 AM
  4. Modifying cabinet temps
    By james in forum Fundamentals
    Replies: 16
    Last Post: 01-05-2002, 08:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •