Thread: water pressure tool [chillers]
05-05-2009, 09:33 PM #1
Can anybody help i am after a water pressure gauge to carry with me to make sure i have correct pressure when on site as some sites i have come across have none fitted. cheers.
05-05-2009, 10:55 PM #2
Re: water pressure tool [chillers]
If you are looking for differential measurement across the chiller or commissioning valves then check out these people, they've been doing it for years and years.
http://www.poddymeter.co.uk/Brian - Newton Abbot, Devon, UK
08-05-2009, 08:53 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
For chillers, correct pressure is not that important, regular analog water pressure gauge with 0,1 bar resolution and class 2 accuracy is good enough.
Important is correct flow, which need flow measuring instrument. Best is to use one of major flow regulation valve manufacturers (Danfoss, Herz etc...) because you usually deal with them, and if you measure their flow you don't need to calculate anything since everything is stored in their memory.
08-05-2009, 11:08 PM #4
sounds like you need a binder gauge, one that you stab in to check differential pressure across the coil?
al
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
PT chart for different elevations
By dkalasz in forum Tools and CalculatorsReplies: 84Last Post: 20-07-2008, 05:09 PM -
Water Chiller Gas Pressure ??
By rajpatel in forum CommercialReplies: 6Last Post: 14-05-2008, 12:41 AM -
Psychrometrics
By Prof Sporlan in forum FundamentalsReplies: 12Last Post: 01-12-2001, 06:48 PM