    refrigerant pipe installation practice



    Hi guys,
    I still don't get it why we don't insulate liquid lines in split a/c application. Is this has something to do with subcooling?

    According to my analysis, since liquid is formed through heat rejection in the condenser, it will have a tendency of removing more heat while it is exposed to ambient till it reaches to the evaporator unit.

    In that case what if the ambient is too hot? boiling temperature of a R407c is -42 degC.

    I really don't have a clear explanation on this. So if someone out there can explain it well, I would appreciate.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: refrigerant pipe installation practice

    This is an interesting subject...

    If the liquid line is warmer than the ambient temperature it is rejecting heat to the air. That is a good idea. If the liquid line is insulated the insulation slows down the heat rejection, which would not be helpful.

    If the liquid is colder than the ambient temperature and the line is not insulated the pipe will absorb heat from the ambient and reduce the subcooling. Again, this is not helpful.

    IMO, this is a matter of heat transfer and accomplishing what you need to ensure the refrigeration system performs as designed.
    If all else fails, ask for help.


  3. #3
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: refrigerant pipe installation practice

    I think that heat transfer won't be significant(one direction or another). Heat transfer coefficient is low(air and natural convection). Surface of the liquid pipe is small(no fins). Temperature difference between liquid refrigerant and ambient air isn't significant as well.

  4. #4
    Join Date
    Apr 2009
    Location
    Dubai, UAE
    Age
    42
    Posts
    16
    Rep Power
    0

    Re: refrigerant pipe installation practice

    I would agree with iceman and would agree with segei as well. It will have a minimal amount of heat rejection or absorption because of no fins and forced convection. Heat transfer coefficient on copper is good for conduction but on natural convection it is minimal.

    As per our design, the condensing temperature is at 60 degC & ambient is 43 degC. So it is reasonable to have our liquid line un-insulated.

    Thanks to you both Segei & Iceman.

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: refrigerant pipe installation practice

    I thought at the outlet of condensor ,the liquid line has a orifice so liquid line is always cool ( like a pre expansion ) . Don't know the reason as its just part of its dasign .
    That is why it is insulated .

  6. #6
    Join Date
    Apr 2009
    Location
    Dubai, UAE
    Age
    42
    Posts
    16
    Rep Power
    0

    Re: refrigerant pipe installation practice

    Correction, that 60 degC condensing temp is at saturated vapour line. So the temperature may go down to certain degree wether below of that 43 degC ambient or above. The software Coolpack can tell its exact liquid saturated temp.

    I never thought an orifice would also installed at the outlet side of the condenser. As far as i know it is only in evaporator. If it is used as a pre-expansion then that would dropped down the pressure without enough subcooling.

    By the way guys, how can you decide whether that subcooling or superheating is enough for that design? Do you have reference or formula? I've been searching for its formula but find none.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: refrigerant pipe installation practice

    If the saturated condensing temperature is 60°C and the condenser provides no subcooling, then the liquid leaving the condenser is 60°C. In an ambient of 43°C there is a 17° temperature difference. I agree the heat transfer is minimal by convection or radiation but it does exist nonetheless. Therefore in this example the liquid line is trying to subcool as much as the temperature difference and heat transfer mechanism will allow.

    This whole argument though is based on the liquid line in a purely horizontal plane where you are only dealing with pressure loss due to friction in the pipe & fittings. If the liquid line flows in an upward direction you will need more subcooling to offset the static head penalty (and that is larger than the friction loss in a well designed piping system!).
    If all else fails, ask for help.


  8. #8
    Join Date
    Apr 2009
    Location
    Dubai, UAE
    Age
    42
    Posts
    16
    Rep Power
    0

    Re: refrigerant pipe installation practice

    Iceman,
    Theoretically it will come out the same pressure & temperature on the condenser but if you look on the p-h diagram of R407c (for example) the temperature is slightly offset & will have different saturated liquid & vapour temperature. This thing confuses me though I would still agree with same temperature & pressure.

    Regarding the subcooling & superheating, I'm talking about deciding the value of it. Like if I have a certain design should I just decide to have 2 degC subcool & 5 degC superheat so I can get an analysis in p-h diagram?

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: refrigerant pipe installation practice

    I did not consider the glide so there can be slight differences of course. I was thinking of a pure refrigerant or azeotrope.

    Quote Originally Posted by jedax81
    Regarding the subcooling & superheating, I'm talking about deciding the value of it. Like if I have a certain design should I just decide to have 2 degC subcool & 5 degC superheat so I can get an analysis in p-h diagram?
    Do not use arbitrary values. The amount of subcooling required is determined by the friction loss and/or static head penalty of the liquid line size and installation. You need just enough subcooling to ensure the liquid quality is 100% liquid to obtain the rated capacity.

    However, if you provide additional subcooling the TXV capacity can increase which may be helpful.

    Superheat: you need just enough to keep liquid out of the compressor. More is bad...
    If all else fails, ask for help.


  10. #10
    Join Date
    Mar 2009
    Location
    Oregon Coast
    Posts
    56
    Rep Power
    16

    Re: refrigerant pipe installation practice

    Iceman, your are so right, now, if I could just get customers to understand that. In my line of work, commercial fishing, the users always want to tweak the settings. The hardest thing to make them understand is ice forming on the suction valve of the compressor is not a bad thing.

  11. #11
    Join Date
    Oct 2008
    Location
    Southwest Scotland
    Posts
    51
    Rep Power
    16

    Re: refrigerant pipe installation practice

    Hi Im now in my 3rd year of refrigeration and wondering if you would clarify what I have taken this thread.

    If you have sufficent sub cooling to Just fill the sight glass, you should work out pressure drop from the sight glass (including pipe length, bends and componants) to the TEV and add subcooling equivilant to the comparative temperature to compensate?
    Last edited by Bachuss; 27-10-2010 at 12:44 PM. Reason: Half sentances and poor spelling, my speciality!

  12. #12
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: refrigerant pipe installation practice

    On a single compressor circuit: Sight glass should be right next to the Liquid Solenoid, which is itself the biggest player in causing vapor generation upstream of the TXV.

    But the objective remains: The liquid should remain liquid state until the Expansion point....And thus a little subcooling is required. On an Air Cooled System: the condensing liquid is itself always going to be warmer than the air going over the condenser and you will not be able to "ambient subcool" to anything below that temperature, so the only thing that can happen in a liquid line run through that same air is that the liquid gets cooler. IF THE CONDENSATE LINE NEEDS TO RUN THROUGH A WARMER THAN AMBIENT SPACE it should be insulated...otherwise it should not be.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Measurement of pipe lengths
    By batfink in forum Technical Discussions
    Replies: 11
    Last Post: 23-09-2008, 09:50 PM
  3. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •