    Re: R407 C wall mount LG 7 Kw



    G'day from New Zealand Aiyub,
    I would start again, evacuate, and weigh the correct charge into the system, and then you will know you have the right amount of gas, I also think you have a faulty indoor sensor, hope this helps
    Regards
    Tony



  2. #52
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: R407 C wall mount LG 7 Kw

    Hello Tony,

    This " beast" is rearing its head up again, but youre absolutely right...... Just shows, The Kiwis got their heads screwed on right.

    I have removed all the charge, fresh charge is in..........and the unit is working swimmingly.

    But I have given the unit a head start.......I have now connected condenser fan direct, ie: it is no longer controlled by the whims of the indoor unit sensor...........( which as u say, could well be faulty)

    But I am sick to my back teeth, ( assuming it is faulty, that is ) of LG stuff playing up.........when it should be new????

    I have had three remote controllers pack up.........Yes three. The LCD displays play up.......

    Then this beast........which I refer to as the most unforgiving air con ever built.

    Why would or should you need to have a Masters Degree to comprehend the workings of an air con????

    In this case.........LG dont have the foggiest how to design an air con which uses R407C

    I rest my case.

    Other members............may shake their heads at my impertinence.............but , me...........LG and I are not in Love no more.........we are seeking a divorce.......

    And pssssssssss,, between you and I, I have a secret mistress/ girlfreind on the side !!!!

    Her name is..........Fuji.....and Mitsi !!!! but one blinked at me the other day.........her name is Tosh !!!!

  3. #53
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23

    Wink Re: R407 C wall mount LG 7 Kw

    Daikin

  4. #54
    david mcbain's Avatar
    david mcbain Guest

    Re: R407 C wall mount LG 7 Kw

    can i just ask if the low ambient controll is set correctly and that you have run this unit with a probe taking evap temp if not please could you as i am interested as to what super heat you have

  5. #55
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: R407 C wall mount LG 7 Kw

    I think u will find the readings somewhere along the thread........This unit is not fitted with Low Ambient Kit

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Fujitsu wall controller
    By iceman007 in forum Air Conditioning
    Replies: 4
    Last Post: 02-03-2006, 04:32 PM
  2. R407 refrigerant
    By JCole21961 in forum Refrigerants
    Replies: 10
    Last Post: 29-08-2005, 05:25 PM
  3. R22 in a R407 system
    By Abe in forum Refrigerants
    Replies: 9
    Last Post: 20-06-2003, 08:51 AM
  4. Cold wall vs. Forced-Air, which is better?
    By pezagent in forum Technical Discussions
    Replies: 4
    Last Post: 23-05-2003, 04:34 AM
  5. Mitsu High Wall
    By Abe in forum Air Conditioning
    Replies: 4
    Last Post: 07-05-2002, 05:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •