Results 51 to 55 of 55
Thread: R407 C wall mount LG 7 Kw
-
05-07-2004, 03:25 AM #51
Re: R407 C wall mount LG 7 Kw
G'day from New Zealand Aiyub,
I would start again, evacuate, and weigh the correct charge into the system, and then you will know you have the right amount of gas, I also think you have a faulty indoor sensor, hope this helps
Regards
Tony
-
05-07-2004, 10:13 PM #52
Re: R407 C wall mount LG 7 Kw
Hello Tony,
This " beast" is rearing its head up again, but youre absolutely right...... Just shows, The Kiwis got their heads screwed on right.
I have removed all the charge, fresh charge is in..........and the unit is working swimmingly.
But I have given the unit a head start.......I have now connected condenser fan direct, ie: it is no longer controlled by the whims of the indoor unit sensor...........( which as u say, could well be faulty)
But I am sick to my back teeth, ( assuming it is faulty, that is ) of LG stuff playing up.........when it should be new????
I have had three remote controllers pack up.........Yes three. The LCD displays play up.......
Then this beast........which I refer to as the most unforgiving air con ever built.
Why would or should you need to have a Masters Degree to comprehend the workings of an air con????
In this case.........LG dont have the foggiest how to design an air con which uses R407C
I rest my case.
Other members............may shake their heads at my impertinence.............but , me...........LG and I are not in Love no more.........we are seeking a divorce.......
And pssssssssss,, between you and I, I have a secret mistress/ girlfreind on the side !!!!
Her name is..........Fuji.....and Mitsi !!!! but one blinked at me the other day.........her name is Tosh !!!!
-
06-07-2004, 06:22 AM #53
Re: R407 C wall mount LG 7 Kw
Daikin
-
12-07-2004, 02:53 PM #54
Re: R407 C wall mount LG 7 Kw
can i just ask if the low ambient controll is set correctly and that you have run this unit with a probe taking evap temp if not please could you as i am interested as to what super heat you have
-
12-07-2004, 10:35 PM #55
Re: R407 C wall mount LG 7 Kw
I think u will find the readings somewhere along the thread........This unit is not fitted with Low Ambient Kit
Similar Threads
-
Fujitsu wall controller
By iceman007 in forum Air ConditioningReplies: 4Last Post: 02-03-2006, 04:32 PM -
R407 refrigerant
By JCole21961 in forum RefrigerantsReplies: 10Last Post: 29-08-2005, 05:25 PM -
R22 in a R407 system
By Abe in forum RefrigerantsReplies: 9Last Post: 20-06-2003, 08:51 AM -
Cold wall vs. Forced-Air, which is better?
By pezagent in forum Technical DiscussionsReplies: 4Last Post: 23-05-2003, 04:34 AM -
Mitsu High Wall
By Abe in forum Air ConditioningReplies: 4Last Post: 07-05-2002, 05:59 PM