    R407 C wall mount LG 7 Kw

    Need an insight into this one. Last year installed an LG Wall Mount, 7Kw Cooling only R407C

    In my opinion it was never as cold as I thought it should be, I put it down to the gas. never mind.........got a call today, unit is struggling

    I hooked up gauges, back pressure is settled on around 2.7 Bar..........then condenser fans cut, I hear a whooshing sound as if a solonoid has opened..........back pressure zooms up to +8 Bar..........condenser fans cut back in and back pressure starts going back to 2.75 Bar again

    After a while compressor and fans stop...............after a while restart again

    Any ideas anyone??

  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R407 C wall mount LG 7 Kw

    I am assuming this is an A/C unit?

    This sounds like a defrost cycle.

    Have you taken a full list of temp measurements?

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: R407 C wall mount LG 7 Kw

    Hi Abe,

    I agree with Gary. If it goes into defrosting cycle when its hot out, check the charge. Another problem that I would check, is the evaporator coil temp sensor. You should check its resistance to see if it is function OK. That sensor is responsible of defrost in cooling mode.

    Another thing that comes to mind. Does the compressor works all the time?
    You say its cooling only so there might not be a 4 way valve in the condensing unit.

    Chemi

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R407 C wall mount LG 7 Kw

    Given the low back pressure/low SST (about 21F), I would say the sensor is just doing it's job.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: R407 C wall mount LG 7 Kw

    Yes Gary, but if its cooling only unit then I doubt if there a 4 way valve to preform the defrost.

    Faulty compressor comes to mind, the sound Abe describes is a scroll stopping and starting.

    Chemi

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R407 C wall mount LG 7 Kw

    A full list of temp measurements would clearly tell the story.

Similar Threads

  1. Fujitsu wall controller
    By iceman007 in forum Air Conditioning
    Replies: 4
    Last Post: 02-03-2006, 04:32 PM
  2. R407 refrigerant
    By JCole21961 in forum Refrigerants
    Replies: 10
    Last Post: 29-08-2005, 05:25 PM
  3. R22 in a R407 system
    By Abe in forum Refrigerants
    Replies: 9
    Last Post: 20-06-2003, 08:51 AM
  4. Cold wall vs. Forced-Air, which is better?
    By pezagent in forum Technical Discussions
    Replies: 4
    Last Post: 23-05-2003, 04:34 AM
  5. Mitsu High Wall
    By Abe in forum Air Conditioning
    Replies: 4
    Last Post: 07-05-2002, 05:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •