    daiking help



    hi guys

    im trying to get my head around commissioning of daikin vrv with a scenario as follows:


    1 condender to 4 indoor units. but only one remote controller between all 4 units? (not a centrallized one)

    how does the condenser know there is 4 units? do i have to change address settings? where are they? i know on other makes there are dials on each unit.

    i cant seem to find anything in the manuals.

    where is best to start as i want all units to be picked up and tested (all units will run at the same time)


    many thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daiking help

    Which manual are you looking at?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: daiking help

    As long as you have wired it correct the unit will self address.
    there is only four units so if it all starts then all is well. If you want to check each units performence then the easiest way is to press and hold the inspection test button for around 5 seconds twice in turn and get into service mode 41, using the timer up and down and temp buttons you can schroll through sensor readings for each each fan coil, this should be highlighted in the service manual for Daikin units.

  4. #4
    Join Date
    May 2009
    Location
    Portugal
    Age
    60
    Posts
    14
    Rep Power
    0

    Re: daiking help

    From "H" VRV series onwards (H, K, L, M and P series) there's no need to adress manually, the indoors as well as outdoors will adress automatically.