    floor cooling issue



    Hi sirs

    Floor heating is widely applied but I've seen very few cases about floor cooling application. How about your ideas on the floor heating and cooling system? Is it good way to use floor embeded tube as heating and cooling terminal? Welcome your input. Thx!

    rgds
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: floor cooling issue

    Cold air will sit at the floor.

  3. #3
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: floor cooling issue

    Most of our facility's use glycol heated from the ammonia hot gas, then pumped through plastic piping, the piping is layed in the sub floor below the insulation thus keeping it at a specified temperature. As long as it stays above freezing there should not be any problems with the floor heaving. Hopefully I have made it clear to all. If you need a further explanation maybe I can elaborate a little better.

  4. #4
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    82
    Rep Power
    18

    Re: floor cooling issue

    I have commissioned a Mitsu "heat pump boiler" system as part of a City Multi VRF installation. The wet side provided under floor heating & cooling to a private residence, the heating side went through a UK winter without major issues, however we are yet to hear if it is quite so effective if we get a decent summer..... I have my reservations!!

    "I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: floor cooling issue

    Hot air rises, cold air doesn't; how will cool air mix with room air to provide comfort cooling?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: floor cooling issue

    Hi Lc shi
    Good to talk with you again. Three years ago I commissioned a building with an atrium six stories high which used underfloor heating and cooling. we use an air speed sensor near the top and several temp sensors at various levels. For this application the process worked well and is efficient in controling temp in the occupied zone.

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: floor cooling issue

    Hi Tesla
    Nice to see you again! Your information is valuable. thx!

    LC
    I hear...I forget;I see...I remember;I do...I understand

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: floor cooling issue

    Quote Originally Posted by Tesla View Post
    Three years ago I commissioned a building with an atrium six stories high which used underfloor heating and cooling. we use an air speed sensor near the top and several temp sensors at various levels. For this application the process worked well and is efficient in controling temp in the occupied zone.

    Could you tell us how looks temperature distribution by height in place cooled with floor cooling and do you have to adjust set point constantly to avoid moisture condensation at floor.
    Does house need to be heavily insulated so that temperature difference between indoor air and floor is low.

  9. #9
    Join Date
    Mar 2007
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: floor cooling issue

    under floor cooling does not really work, condensation from over cooling is a major fault, because of this the temp difference between the floor and the room abient is at best 10degC.
    with reference to air movement, any surface which is warmer than the ambeint temperature will create a natural up draught, for example a person.
    in the early 90s a company was marketing a ventilation system that used very low velocity air that was distributed at low level, this worked in a similar priciple, but large air volumes were required.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: floor cooling issue

    Quote Originally Posted by milkybar33 View Post
    under floor cooling does not really work, condensation from over cooling is a major fault,....
    Not if you control via a dewpoint measurement
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. computer& communication room ac's reliability issue
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 13-04-2009, 10:19 AM
  2. Flood back issue?
    By Arc in forum Trouble Shooting
    Replies: 15
    Last Post: 28-10-2008, 03:40 PM
  3. r22 replacement issue -emergent
    By Lc_shi in forum Refrigerants
    Replies: 3
    Last Post: 02-01-2008, 12:10 PM
  4. hydraulic floor heating issue
    By Lc_shi in forum New Technologies
    Replies: 6
    Last Post: 02-01-2007, 09:07 PM
  5. Air conditioning system cleaning issue
    By Lc_shi in forum Legal-Business-Marketing
    Replies: 2
    Last Post: 24-08-2006, 03:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •