    One of the sites had a audit from International firm. They want an explanation on why fresh air in not required in the cold stores like what we provide for Airconditioning.

    Is there any good info on this?

    There is a combination of chiller / freezers in the project.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Fresh air in the Cold stores

    Quote Originally Posted by smpsmp45
    They want an explanation on why fresh air in not required in the cold stores like what we provide for Air conditioning.
    Ventilation is introduced every time a door is opened into the cold store. There is a lot of fresh air each time, which is seen when you perform the door heat load calculations for the infiltration rates. The door loads are usually one of the biggest cooling loads already without adding to that with minimum ventilation requirements.

    Office buildings are very tight and when you factor in the high personal density in an office building the minimum ventilation is required for a good environment. Cold stores on the other hand have a very low people density.

    Was this firm an insurance company or some safety audit?
    If all else fails, ask for help.


  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Fresh air in the Cold stores

    I agree with US ICEMAN,

    Only a comment I want to do:

    If it is cold stores with living products such as fruits, vegetables and so on and if the products are to be storage during much time without service to the cold store so in that case you would to need a ventilator working a "couple" of hours/day to replace the air inside by fresh air outside.

    Regards
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Fresh air in the Cold stores

    Quote Originally Posted by Sandro Baptista View Post
    I agree with US ICEMAN,

    Only a comment I want to do:

    If it is cold stores with living products such as fruits, vegetables and so on and if the products are to be storage during much time without service to the cold store so in that case you would to need a ventilator working a "couple" of hours/day to replace the air inside by fresh air outside.

    Regards

    ERM!
    Living products in a cold store NO!
    In a Chill Room Maybe!
    The whole idea of storing within a cold store at a minimum of -18c.
    Is because everything is inert at that temperature or below.
    Even bacteria cannot exist at these temperatures.
    Consider that meats and vegetables, fruit juices, tobacco etc. etc are shipped all around the world.
    In this environment.
    Add fresh air and the chamber heat load goes through the roof.
    More importantly the stored produce would spoil!
    If this is a customer ask them to pay for dedicated chambers and a disclaimer as to how long the product will keep!
    I have heard some stupid things but this one is tops!
    Grizzly

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Fresh air in the Cold stores

    Quote Originally Posted by smpsmp45 View Post
    One of the sites had a audit from International firm. They want an explanation on why fresh air in not required in the cold stores like what we provide for Airconditioning.

    Is there any good info on this?

    There is a combination of chiller / freezers in the project.
    Why is it required? Do they know the difference between a/c building and cold storage?

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Fresh air in the Cold stores

    Quote Originally Posted by Grizzly View Post
    ERM!
    Living products in a cold store NO!
    In a Chill Room Maybe!
    The whole idea of storing within a cold store at a minimum of -18c.
    Is because everything is inert at that temperature or below.
    Even bacteria cannot exist at these temperatures.
    Consider that meats and vegetables, fruit juices, tobacco etc. etc are shipped all around the world.
    In this environment.
    Add fresh air and the chamber heat load goes through the roof.
    More importantly the stored produce would spoil!
    If this is a customer ask them to pay for dedicated chambers and a disclaimer as to how long the product will keep!
    I have heard some stupid things but this one is tops!
    Grizzly
    I thought that the name cold stores rooms also included the "refrigerated stores" services at +2ºC/0ºC. I'm sorry.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Fresh air in the Cold stores

    Quote Originally Posted by Sandro Baptista View Post
    I thought that the name cold stores rooms also included the "refrigerated stores" services at +2ºC/0ºC. I'm sorry.
    No need to apologise Sandro.
    Basically a cold store is either, so you were correct if WE interpret the original question the way you did.
    I would tend to call that a chill room.

    Sorry from me, if I appeared to have a go at you.
    Still we have managed to clarify a few things hopefully?
    Grizzly

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Fresh air in the Cold stores

    Here is another example of why we have so many issues in this business. We have too many names for things that can be used to indicate the same thing or something different depending on where you come from in the world.

    I'm not saying either is wrong, only that each can mean something different to other people. And, when we use the terms we are familiar with someone else may have a completely different idea of their definition.

    cold stores rooms & refrigerated stores
    If all else fails, ask for help.


  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Fresh air in the Cold stores

    Quote Originally Posted by US Iceman View Post
    Here is another example of why we have so many issues in this business. We have too many names for things that can be used to indicate the same thing or something different depending on where you come from in the world.

    I'm not saying either is wrong, only that each can mean something different to other people. And, when we use the terms we are familiar with someone else may have a completely different idea of their definition.

    cold stores rooms & refrigerated stores
    Your to kind to us all Ice!
    Your Moderator traits are showing!
    Perhaps smpsmp45 can answer the question for us all?
    Grizzly

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Fresh air in the Cold stores

    Just trying to keep it friendly!
    If all else fails, ask for help.


  11. #11
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Fresh air in the Cold stores

    YOu may be surprised that this issue came up at Mcdonalds big warehouse. The info provided by all is fine & good enough, but you know auditors, if they get a reference from a book/ handbook, that is good enough for them.

    I shall compile all these points to see if they are satisfied.

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Fresh air in the Cold stores

    Quote Originally Posted by smpsmp45
    ...if they get a reference from a book/ handbook, that is good enough for them.
    Yeas, at that is part of the problem. These people come in as outside hired experts and they do not know enough to do a good job. The result is what you describe. A consultant who reads something and expects it to apply to any and all things regardless of the application or intended use.

    It's what we call boiler plate language to show how thoughtful they are when reviewing someone's building. And by reference to this language they show how complete their review is.

    It is always interesting when this occurs!
    If all else fails, ask for help.


  13. #13
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Fresh air in the Cold stores

    Dear US ICEMAN

    You have nice way of putting up the things. I was just referring to your posts on Ammonia DX systems & it was very nicely written

  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Fresh air in the Cold stores

    Thank you. i just say what I think...

    One benefit of getting older is you learn something new every day. The downside of getting older is you have more things to forget.
    If all else fails, ask for help.


  15. #15
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Fresh air in the Cold stores

    Quote Originally Posted by US Iceman View Post
    Thank you. i just say what I think...

    One benefit of getting older is you learn something new every day. The downside of getting older is you have more things to forget.
    I agree with you ICE MAN
    To make progress is never good enough, I want to do better and better and better

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Fresh air in the Cold stores

    There is a great saying about consultants, and auditors drop into same league.
    "consultants are the ones that come out of the hills and kill all the wounded after the battle is over. "
    magoo

Similar Threads

  1. fresh air heating in cold area
    By Lc_shi in forum Air Conditioning
    Replies: 7
    Last Post: 14-05-2009, 01:37 AM
  2. Replies: 2
    Last Post: 06-04-2009, 04:30 AM
  3. Structural columns in the cold stores
    By smpsmp45 in forum New to RE
    Replies: 11
    Last Post: 06-10-2007, 11:42 PM
  4. Multiple ref. units for cold stores
    By smpsmp45 in forum Commissioning
    Replies: 12
    Last Post: 21-06-2007, 06:02 PM
  5. lighting in cold stores
    By smpsmp45 in forum Electrical
    Replies: 0
    Last Post: 29-05-2007, 01:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •