26-04-2009, 11:53 AM #1
new cold room new refrig system!
Hello all, when you have built a new system from scratch, i.e. brand new cold room/refrigeration system, and fitting / brazing new pipework etc, would you have to carry out a triple evacuation??
Thanks in advance
-
26-04-2009, 01:35 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: new cold room new refrig system!
Triple evacuation could speed drying of system. If you are not satisfied with speed of your evacuation or you have lot of moisture in system, then triple evacuation is beneficial.
That all depend on actual situation.
-
26-04-2009, 11:42 PM #3
Re: new cold room new refrig system!
Not my normal work load but I would suggest that it is a good practice as coldroom downtime due to a poor install can be costly in both time and money.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
25-06-2009, 12:57 AM #4
Re: new cold room new refrig system!
i do a good few installs on coldrooms never do a triple vac just a good strength test and good vac(400-500 micron) unless i did not install pipework but might not be a bad practice.but never had a coldroom go down(touch wood) due to vac procedure
Last edited by sean1; 25-06-2009 at 12:59 AM.
-
26-06-2009, 03:24 AM #5
Re: new cold room new refrig system!
triple evacuations went out the door when gas management legislations where introduced here.most triple evacuations where related to domestic applications in my day.
mmm to beer or not to beer...........lets drink breakfast
-
01-07-2009, 11:31 AM #6
Re: new cold room new refrig system!
i normally check all my joints as i go as you do... pressurize system with nitrogen when complete check for pressure drop/leaks before evacuating system charging and commissioning.
"Old fridgies never die, they just run out of gas!"
Similar Threads
-
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Cold Room Design - minus 25deg C
By vijay_study in forum FundamentalsReplies: 34Last Post: 11-11-2009, 07:12 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Calculating Refrigeration load for Cold room
By Sridhar1312 in forum CO2Replies: 1Last Post: 16-01-2008, 12:06 AM -
Cold room box required
By Andy W in forum CommercialReplies: 2Last Post: 19-07-2006, 08:48 PM