Results 1 to 9 of 9
Thread: oil changing
-
25-04-2009, 09:29 AM #1
oil changing
hi everybody I want to know the procedure of changing lubrication oil for semi-hermatic compressor any advice please.
-
25-04-2009, 10:53 AM #2
Re: oil changing
1. Close suction valve.
2. Switch on compressor and force it to 0 psig.
3. Switch off power.
4. Close discharge valve.
5. Open gauges to release any pressure left inside the compressor.
6. Open oil cap, pull out oil filter and holding spring and let all the old oil come out.
7. Inspect the old oil for any suspicious particles.
8. Insert back filter and spring, put a new gasket.
9. Fill with new oil.
10. Evacuate.
11. Open discharge valve.
12. Switch on power.
13. Open suction valve and let compressor run.
-
26-04-2009, 07:11 PM #3
Re: oil changing
if the tip from Chemi is not working, look up the manual from the manufacturer.
Ice
-
26-04-2009, 07:14 PM #4
Re: oil changing
hey Chemi, dos nr4 comes not just a split second before nr3 ;-))
Ice
-
28-04-2009, 02:27 AM #5
Re: oil changing
The procedure already given is OK, but doesn't take into account if the system has an oil sep. Sometimes using this method, gas can pass back into the crankcase through the oil return line. It is necessary in some cases to remove the oil return line from the compressor and quickly put a capped fitting onto it. Then when oil has been changed put a rag over it and remove the cap and refit to compressor. But the latter is risky and the safer option is to recover the gas then when done change drier and put the old gas back in.
Hope this helps,
Murray.
-
28-04-2009, 03:26 AM #6
Re: oil changing
hi all &thanks to chemi-cool the procedure is ok.
-
28-04-2009, 01:35 PM #7
Re: oil changing
am i being rude but went through all posts and i think we are bringing jebar through his apprenticship... if you cant do an oil change then your boss should know!!... there are enough cowboys giving this game a bad name ... if you need help then this is the place with some fantastic guys giving words of wisdom...DONT ABUSE IT!!.. ok venting over
-
28-04-2009, 01:44 PM #8
Re: oil changing
remove the oil return line from the compressor and quickly put a capped fitting onto it.
BTW, I always connect the oil return line to the suction line before the accumulator.
icecube51,
I don't know about you but I never close the discharge valve when power is on.[ Even if compressor is still]
-
02-05-2009, 10:47 AM #9
Re: oil changing
hey Chemi-cool,
if you close the discharge valve when power is of,then you risk to get a flow-back,thats why i close the valve a split second before i cut of the power.
its not to prove you are wrong,just looking if i am wright.
Ice
Similar Threads
-
changing refrigerant
By ximi in forum Technical SpeculationsReplies: 2Last Post: 21-03-2009, 12:23 AM -
Changing from 507 to 22 in a cold store.
By babs jolayemi in forum CommercialReplies: 2Last Post: 24-02-2009, 09:08 PM -
changing r22
By aza in forum RefrigerantsReplies: 4Last Post: 16-04-2008, 07:57 PM -
Procedure for changing compressor (134a) please
By Egan Technical in forum DomesticReplies: 7Last Post: 10-02-2008, 12:03 AM -
changing to automatic valve
By donato in forum Technical SpeculationsReplies: 2Last Post: 29-07-2006, 12:50 PM