    Evaporator too big.



    To all

    Let's suggestion to me , How the system occur ? , when we applide of the biger evaporator than system ( Compressor 25 kw cooling cap , Evap Coil 45 kw cooling cap).

    Thank you for all kindness.



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Evaporator too big.

    Quote Originally Posted by nuntachai View Post
    To all

    Let's suggestion to me , How the system occur ? , when we applide of the biger evaporator than system ( Compressor 25 kw cooling cap , Evap Coil 45 kw cooling cap).

    Thank you for all kindness.
    Hi nuntachi,

    Let see if I understand: you want to know what's the behave of a refrigerant plant when we have a compressor and a evaporator with differente capacities, right?

    Well, I give you an example:

    Suppose you have the following project parameters:

    - Air cold store temperature: -25ºC
    - Evaporating temperature: -32ºC

    Now suppose that we have a compressor that at -34ºC (2 K suction loss, for instead) of pressure suction equivalent saturation temperature regime will give 25 kW.
    And you have a aircooler evaporator that will give 45 kW at -25ºC (air temperature) and at -32ºC evaporating temperature.

    The system will reach an equilibrium between compressor and evaporator which will result in a refrigerant capacity of the system that will be bigger than 25 kW and less than 45 kW. This happens because:
    • Less than 45 kW because you can mantain the DT = 7K since you have only 25 kW of compressor capacity;
    • Bigger than 25 kW because the suction pressure in the compressor will rise (» bigger evaporating temperature) due the fact that the aircooler can give more than 25 kW at a DT less than 7K at -25ºC cold store temperature.
    I hope have been clear.

    Regards

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Evaporator too big.

    Quote Originally Posted by Sandro Baptista View Post
    Hi nuntachi,

    Let see if I understand: you want to know what's the behave of a refrigerant plant when we have a compressor and a evaporator with differente capacities, right?

    Well, I give you an example:

    Suppose you have the following project parameters:

    - Air cold store temperature: -25ºC
    - Evaporating temperature: -32ºC

    Now suppose that we have a compressor that at -34ºC (2 K suction loss, for instead) of pressure suction equivalent saturation temperature regime will give 25 kW.
    And you have a aircooler evaporator that will give 45 kW at -25ºC (air temperature) and at -32ºC evaporating temperature.


    The system will reach an equilibrium between compressor and evaporator which will result in a refrigerant capacity of the system that will be bigger than 25 kW and less than 45 kW. This happens because:
    • Less than 45 kW because you can mantain the DT = 7K since you have only 25 kW of compressor capacity;
    • Bigger than 25 kW because the suction pressure in the compressor will rise (» bigger evaporating temperature) due the fact that the aircooler can give more than 25 kW at a DT less than 7K at -25ºC cold store temperature.
    I hope have been clear.

    Regards

    I forget to complete my thought : I estimate an capacity (in the equilibrium of the system) of maybe about 30 kW.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator too big.

    Compressor capacity will be the same at same evaporation and condensation temperatures because it is determined by refrigerant density and compressor displacement (mass flow).
    For compressor it doesn't matter how big is evaporator if evaporation (and condensation) temperatures are not changed.

    But fact is that at same cell temperature, bigger evaporator will have smaller TD, and that evaporation temperature will be higher than with smaller evaporator.
    That higher evaporation temperature mean that compressor have higher capacity than with lower evaporation temperature achieved with smaller evaporator (because of his higher TD).


    But, we need to keep humidity in control, and that is determined by TD. Therefore, it is essential to match evaporator and compressor to achieve targeted humidity in refrigerated space.
    Did I complicated or cleared things?
    Last edited by nike123; 25-04-2009 at 10:34 AM.

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evaporator too big.

    Quote Originally Posted by nike123 View Post
    But fact is that at same cell temperature, bigger evaporator will have smaller TD, and that evaporation temperature will be higher than with smaller evaporator.
    That higher evaporation temperature mean that compressor have higher capacity than with lower evaporation temperature achieved with smaller evaporator (because of his higher TD).

    But, we need to keep humidity in control, and that is determined by TD. Therefore, it is essential to match evaporator and compressor to achieve targeted humidity in refrigerated space.
    Did I complicated or cleared things?
    I agree. The oversize evaporator, with higher saturation temp, can mean that the compressor has to work much harder. It also then leads to higher compressor discharge temperatures.

    For a heat-pump, this becomes a real issue, I've found.

    Sometimes (?often?) ex refrigeration/aircon designers merrily oversize the evaporator for a heat-pump - but, this can lead to major system imbalances & reduction in COP off the optimum thermodynamic COP value.

    Best to finely match evap/compressor/condenser specifically to your target application.
    Last edited by desA; 25-04-2009 at 12:50 PM.

  6. #6
    Join Date
    Jul 2008
    Location
    Thailand
    Age
    51
    Posts
    12
    Rep Power
    0

    Re: Evaporator too big.

    Thank a lot, Sandro
    It quite clear.

  7. #7
    Join Date
    Jul 2008
    Location
    Thailand
    Age
    51
    Posts
    12
    Rep Power
    0

    Re: Evaporator too big.

    Hi nike123 and thank you for suggestion......
    nike123 , when temperature of evaporator higher(higher than smaller evaporator) ,that meaning heat reject at the condenser will be increasing?

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evaporator too big.

    ^ Yes, and then some. The COP will also probably reduce, since the compressor work will, in all likelihood, increase excessively.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporator too big.

    Quote Originally Posted by nuntachai
    ...that meaning heat reject at the condenser will be increasing?
    Yes.

    If the larger evaporator is used the compressor suction pressure will be higher. This results in greater cooling capacity for the reasons nike123 provided. With the increase in compressor capacity, the heat rejection also increases. This may require you to provide a larger condenser also!
    If all else fails, ask for help.


  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evaporator too big.

    The compressor manufacturer may often have a table, or software program, where compressor/evaporator/condenser duties are matched at a certain set of operating conditions (evaporator Tsat, condenser Tsat).

    Copeland & Bitzer provide useful software for this.

    As I see it, the heart of the refrigeration process is really the compressor, with the evaporator & condenser sized to fit around this.

  11. #11
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Evaporator too big.

    Quote Originally Posted by nike123 View Post
    But, we need to keep humidity in control, and that is determined by TD. Therefore, it is essential to match evaporator and compressor to achieve targeted humidity in refrigerated space.
    Taking the example I have done at my first post (Air temperature cold store = -25ºC, Evaporating temperature = -32ºC) if you have a used existing bigger evaporator that you want to install that will low the DT, as have told, so less water vapor of the air will condensing in the cold coil » higher relative humidity. For a freezer cold store, a bigger H.R. 90%, for instead, is positive. Picking again the example I have done the evaporating would increase to about -30ºC » DT = 5K is completely acceptable.

    If you don't need to keep low the humidity, having a bigger evaporator doesn't do warm at all, it will guarantee a bigger relative humidity, wich is desired for most applications.
    To make progress is never good enough, I want to do better and better and better

  12. #12
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Evaporator too big.

    Quote Originally Posted by desA View Post
    I agree. The oversize evaporator, with higher saturation temp, can mean that the compressor has to work much harder. It also then leads to higher compressor discharge temperatures.

    For a heat-pump, this becomes a real issue, I've found.

    Sometimes (?often?) ex refrigeration/aircon designers merrily oversize the evaporator for a heat-pump - but, this can lead to major system imbalances & reduction in COP off the optimum thermodynamic COP value.

    Best to finely match evap/compressor/condenser specifically to your target application.

    I don't agree with you.

    Keep in mind that if the condenser is selected to have the same condensation temperature parameter of design I can ensure that is not true. Come on...about what you said "that the compressor has to work much harder"we are talking in an increasing of about a few degrees of higher evaporting temperature (maybe 2...3K of higher evaporating temperature). The COP will be higher, the discharge temperature will be lower because the ratio of the absolute pressure will be smaller (p_cond/p_suction) and the compressor will work little bit less time.
    Of course that the due the fact that the suction pressure will be a little higher the connection rods, the cranck shaft and piston rods will be little more subject to mechanical tensions but is not relevant. Possible, in global due the fact the discharge temperature is lower the durability of the compressor will be the same.
    To make progress is never good enough, I want to do better and better and better

  13. #13
    Join Date
    Jul 2008
    Location
    Thailand
    Age
    51
    Posts
    12
    Rep Power
    0

    Re: Evaporator too big.

    Thank a lot for all of you.

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Evaporator too big.

    I may have lost a few details in translation. But get back to basics. Everyone can pontificate to the enth degree. The system has to be balanced.
    Big evaps versus smaller compressors is not unusual, the design eng,, may have required a high sensible heat ratio, or high air flow and a low system TD at the evaporator, what ever. Several things have to be addressed and checked.
    1/ the TEV matches the compressor duty.
    2/ The TEV has [ mop ]
    3/ The distributor orifice and distributor tails are matched to TEV performance.
    4/ The compressor charactoristics can handle high suction pressures at times.
    5/ The condenser duty matches the various conditions of load and ambient conditions.
    6/ The TEV superheat readings have to be checked.
    All above are essential. TEV sizing, and orifice and tail tube sizing can create havic, TEV hunting , liquid slugging, high suction superheat, lack of system performance.
    Until all above are checked and adjusted, the compressor will rev into and early grave.
    magoo

  15. #15
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evaporator too big.

    ^ To add to this, use the Magoo Rule for SH setting:

    SH = (0.6 to 0.7)*TD
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  16. #16
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Evaporator too big.

    In very simple explain. Evaporator Capacity = 45 KW in what TD :Usually TD = 8 to 10:
    if we see 45 KW in 10 TD So For 1 TD it is 4.5 KW
    If your compressor capacity is 25 KW your TD is about 25/4.5
    Do not forget if your evaporator temperature
    Is goes up your compressor capacity also goes up Until 2 of them (( comp. and Evap. )) is come equal.

    Less Td is good for keep humidity in room

  17. #17
    Join Date
    May 2009
    Location
    USA
    Posts
    15
    Rep Power
    0

    Re: Evaporator too big.

    Quote Originally Posted by desA View Post
    ^ To add to this, use the Magoo Rule for SH setting:

    SH = (0.6 to 0.7)*TD

    How is TD calculated in this case??

  18. #18
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evaporator too big.

    TD = Ta,in - Te,sat

    The Kueba site will provide more detail on the computation.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  19. #19
    Join Date
    May 2009
    Location
    USA
    Posts
    15
    Rep Power
    0

    Re: Evaporator too big.

    [quote=desA;162537]TD = Ta,in - Te,sat

    Okay, thanks!

  20. #20
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Evaporator too big.

    My main from TD for Evaporator (Delta T) = Room Temperature – Evaporator Temperature
    Last edited by mbc; 11-10-2009 at 05:37 PM.

  21. #21
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Evaporator too big.

    TD = Ta,in - Te,sat

    This will be TD1



    Room Temperature – Evaporator Temperature will be TDm


    TD1 and TDm could be very different and consequently can give significant difference to the evaporator capacity, specially if the airflow is low and/or the TD is small.
    To make progress is never good enough, I want to do better and better and better

  22. #22
    Join Date
    May 2009
    Location
    USA
    Posts
    15
    Rep Power
    0

    Re: Evaporator too big.

    Quote Originally Posted by Sandro Baptista View Post
    TD = Ta,in - Te,sat

    This will be TD1



    Room Temperature – Evaporator Temperature will be TDm


    TD1 and TDm could be very different and consequently can give significant difference to the evaporator capacity, specially if the airflow is low and/or the TD is small.
    So if i'm following you correctly, TD1 = temp air in - saturated evaporator temperature, whereas TDm is?

    Temp air in should be the same as room temp right? and evaporator temp would be same as saturated evaporator temperature?

    And what is the correct one to use when determining system capacity?
    thanks, AJS

  23. #23
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Evaporator too big.

    Quote Originally Posted by AJS View Post
    So if i'm following you correctly, TD1 = temp air in - saturated evaporator temperature, whereas TDm is?

    Temp air in should be the same as room temp right? and evaporator temp would be same as saturated evaporator temperature?

    And what is the correct one to use when determining system capacity?
    thanks, AJS
    TD1 and TDm generally are the same, but under some circumstances they can differ, for example when air is forced through a warm product and returned directly to the evap.
    Evap temp is higher than SST because you have suction line pressure drops and non useful superheat.
    System Capacity is determined at the compressor (inlet and outlet conditions) Nett refrigeration is based upon conditions entering the TXV and outlet conditions leaving the evap.

  24. #24
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Evaporator too big.

    Quote Originally Posted by mad fridgie View Post
    TD1 and TDm generally are the same, but under some circumstances they can differ, for example when air is forced through a warm product and returned directly to the evap.
    Evap temp is higher than SST because you have suction line pressure drops and non useful superheat.
    System Capacity is determined at the compressor (inlet and outlet conditions) Nett refrigeration is based upon conditions entering the TXV and outlet conditions leaving the evap.
    I' dont agree with the statement TD1 and TDM generally are the same.

    room temperature is the (Tair inlet + Tair outlet) / 2. Is a medium value of the air temperature.

    For example for a TD1 = 8K that could correspond to a TDM of about 7K or 6 K. It depends of the working conditions and the aircooler design.
    To make progress is never good enough, I want to do better and better and better

  25. #25
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Evaporator too big.

    Quote Originally Posted by Sandro Baptista View Post
    I' dont agree with the statement TD1 and TDM generally are the same.

    room temperature is the (Tair inlet + Tair outlet) / 2. Is a medium value of the air temperature.

    For example for a TD1 = 8K that could correspond to a TDM of about 7K or 6 K. It depends of the working conditions and the aircooler design.
    For design purposes you use you design room temperatue as your air on temperature so basically the the same (MOST but not all control there rooms on return air temp. Stat sensor is normally mounted behind the back of the evap coil) I also stated a typical exceptions. Actual room air temperatue varies depending upon where you take the measurement!

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Evaporator too big.

    As I see it, the bottom line overriding factor in all of this is humidity and that relates directly to the coil leaving air temperature. Higher humidity is not always desireable, in which case a larger coil is going to need less airflow and/or face bypass dampers in order to drop the air off temp to achieve humidity targets.

  27. #27
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator too big.

    Hi there,

    Equipment selection is based on design conditions.

    DTe = T(room) - T(evaporation)

    Low DTe like 5°C will result in a bigger evaporator and it will be higher relative humidity in the room.

    High DTe like 10°C will result in a smaller evaporator and lower relative humidity in the room.

    When the evaporator is bigger than this (DTe lower than 5°C) like 2°C then, room temperature and Te will be very close together and superheat will be very small, which in some conditions you will have liquid flood
    back.
    Compare two conditions :
    1- DTe = 8°C , Troom=+2°C then Te=-6°C
    2- DTe=2°C , Troom = +2°C then Te=0°C

    in case 1 compressor will give its capacity at Te=-6°C and in case 2 compressor gives its capacity at Te= 0°C which is higher than case one.

    System will balance itself at the balance point. When you do the balancing calculation then everything is apparent.

    Too big evaporator also is not economically reasonable.


    Practically DTe varies between 5°C and 10°C.


    Cheers
    Even Einstein Asked Questions