Thread: Oil Sump Temp
    Apr 2009
    Colorado
    31
    Oil Sump Temp
    Is there a prefered temp to maintain the oil sump on a Mycom L series compressor ?
    Thanks, Mojjee
    3,357
    Re: Oil Sump Temp
    Not sure if you mean when running or when off .
    If off sump heater on and if has thermostat set it to about 100 - 110 deg F or 35 - 45 deg C
    When comp on about 120 deg F and high oil temp cut out set 150 deg F
    Should have good water flow through oil cooler and heads . If oil cooler water side blocks up it will affect everything , as heads generate more heat too .
    3,357
    Re: Oil Sump Temp
    Just to add minimum oil temp when running should be warm to touch , sump and oil lines .
    Suggest about 80 deg F and oil not foaming . Also oil temp should be approx 20 deg F above saturated suction pressure / temp .
    Jul 2007
    Czech
    61
    374
    Re: Oil Sump Temp
    Minimum oil temperature 30°C, the maximum oil temperature 50°C
    Apr 2009
    Colorado
    31
    Thumbs up Re: Oil Sump Temp
    Thanks, Guys.
  1. Suction gas <-> liquid line heat exchange and performance gains
    Last Post: 18-05-2010, 01:52 PM
  2. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Last Post: 10-05-2008, 04:22 PM
  3. Compressor loading, cooling, and range of operation.
  4. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Last Post: 21-09-2007, 11:46 PM